For discussion only, do not act on this
All the confusion about earth and bonding could be removed at a stroke in the 18th edition.
Re-name the MET as the Main Equipotential Terminal, ban the use of the term "earth wire" and replace it with the true description " Circuit Protective Conductor ".
Then the difference between "bonding" and earthing would dis-appear.
There would still be areas of isolated bonding with no connection, intentional, un-avoidable or accidental, to the MET
At the MET there would be label stating the source of the MET potential, ground rod as in TT, TN-C-S etc and the maximum potential of the MET above true ground.
Make it clear that at times the voltage of the CPC and therefore all bonded ( or as previously ) "earthed" metal work may not be at the same potential as the earth surrounding the house.
It really confused an "electrician" whose clamp meter showed erratic currents in the bond between the Main Earth Terminal and the water supply pipe. He had replaced the undersized bare tinned copper bond and had noticed a spark even though the isolator at the meter was open ( OFF ) At times these currents peaked at over an amp. ( I suspect the peaks were much higher but were averaged by the meter's sampling/damping period. He had at first thought the water pipe ( metallic ) was shorting to something underground. The old hand called out from the firm explained it to him and the slightly worried customer.
All the confusion about earth and bonding could be removed at a stroke in the 18th edition.
Re-name the MET as the Main Equipotential Terminal, ban the use of the term "earth wire" and replace it with the true description " Circuit Protective Conductor ".
Then the difference between "bonding" and earthing would dis-appear.
There would still be areas of isolated bonding with no connection, intentional, un-avoidable or accidental, to the MET
At the MET there would be label stating the source of the MET potential, ground rod as in TT, TN-C-S etc and the maximum potential of the MET above true ground.
Make it clear that at times the voltage of the CPC and therefore all bonded ( or as previously ) "earthed" metal work may not be at the same potential as the earth surrounding the house.
It really confused an "electrician" whose clamp meter showed erratic currents in the bond between the Main Earth Terminal and the water supply pipe. He had replaced the undersized bare tinned copper bond and had noticed a spark even though the isolator at the meter was open ( OFF ) At times these currents peaked at over an amp. ( I suspect the peaks were much higher but were averaged by the meter's sampling/damping period. He had at first thought the water pipe ( metallic ) was shorting to something underground. The old hand called out from the firm explained it to him and the slightly worried customer.