Could be Relay T 31 & T 32 not separating. It would explain why valve only closes when heating stat is satisfied.
Yeah makes sense then, I'll give you an update once the new relay has been fitted.Could be Relay T 31 & T 32 not separating. It would explain why valve only closes when heating stat is satisfied.
Ok I replaced the relay. Everything seemed good it started up I put the thermostat up and the boiler was running. Next I went to go try the hot water tap to see if it would automatically switch for the first time ever and BANG a huge sound from the boiler. I go through turn it off no physical sign of anything burnt etc. But now my flow switch is no longer giving out mains to Terminal 2 when the water is on. So currently I don’t have any hot water now.Could be Relay T 31 & T 32 not separating. It would explain why valve only closes when heating stat is satisfied.
Omg lol I put a 6V AC one in. They look identical though apart from the now obvious writing on the side of the coil. Old one says 230V new says 6V. Where is the isolator fuse and I will check for you, the only fuse I know about is the one in the plug.Are you sure you got correct relay with 240volt coil....Finder 3PCO 6013 8230 0040 cost less than a tenner.
The flow switch only operates the relay coil so nothing to short out ........Wrong voltage coil would go Bang though.. Coil should be about 7.25 kΩ resistance
What size fuse is fitted in isolator. ?
Ok ill give that fuse a double check and make sure its a 5A as it didn't blow.Fuse will be in the plug should be 5a
I would imagine you have fooked the flow switch when the coil fried.
Ok new relay and flow switch is in. Everything is ok and no leaks.Fuse will be in the plug should be 5a
I would imagine you have fooked the flow switch when the coil fried.
Yes I have a wiring diagram. The above wiring you have mentioned is correct.Time to trace the wiring.
Do you have a wiring diagram to follow.
First checks.
M/v Brown wire to T3. T3 to pin 31 on relay ( Common).
L from c/h stat to T on terminal strip. T to relay T 32 (n/c)
I've moved the Red from 3 to T. Will it be OK to try and turn on do you think?If Room stat is across 3 and H then it is bypassing the relay. which explains every thing.
It worked perfectly. Thanks for the help!