Had RCD trouble today, having swapped what read as a healthy circuit onto the RCD side of a SL board.
The RCD didn't trip on switching on, only when certain things were plugged in. The fridge was OK, the freezer on a different circuit (still through the RCD) tripped.
Table lamps tripped the RCD too.
In my experience, a dead neutral/earth short will trip the unit as soon as the circuit is energised. This is obviously not the case!
I finally tracked it down to what appears to be an intermittent NE fault on the GF ring final.
I auto-tested the RCD with the faulty ring in circuit. It failed the 1x test, but passed the others.
However, when I removed the faulty ring from the RCD side, the RCD tested fine.
Can you explain all of this???