Hello,
I have a Danesmoor Utility 15/19 oil boiler with B9B burner and Satronic TF830.3 control box. Boiler sited indoors in upstairs room with outside tank lower than boiler, so Tigerloop fitted. Filter at tank and before boiler. Over 500l of oil in tank.
It had annual service in November - two visits, with changes made including:
Visit 1: new nozzle, tune up, clean and filter checks, new pump with coil, new motor (noisy bearings), new photocell (old one faulty)
Visit 2: new Tigerloop (old unit had failed with oil in upper chamber)
When the boiler runs, it runs very smoothly without problems, and can run for several hours. However, prior to the service, there was an intermittent lock out with the boiler locking out every other day - the engineer has tried to resolve this fault at each service visit in November, but the fault is now worse than before, with lock outs happening at least twice daily. The boiler is programmed to come on for periods of two hours in the early morning and early evening - typically it has locked out when period starts or on first start of programmed period.
Engineer not currently returning calls. Hoping to narrow down cause of fault to get heating running again before it gets colder.
If locked out and there is demand - I press reset on the control box, boiler motor and pump starts, ignition transformer can be heard (and flicker of sparks seen through peephole). Click of oil pump valve is not heard - but magnetic field detector held against coil very briefly lights (under a second) before boiler locks out. No evidence of oil in blast tube or nozzle tip
It typically restarts on second reset - same start up sequence, but click of solenoid valve heard (magnetic field detected and sustained, voltage pen senses increases in voltage from control box to solenoid), flame sustained.
Pump (BFP 21 L3) pressure starts at c100psi, tends to settle at around 92/94 psi with no obvious impact on operation - this is the same when it locks out as when it runs. A little foam in bottom chamber of Tigerloop on first start but reduces to none/very little on longer runs. Causes minor fluctuations in pressure reading but doesn't affect flame establishing/being sustained) and has run on this setup for many years.
I have checked resistance of solenoid coil (071N0810) across bottom two terminals (not open circuit hot or cold), and I have checked resistance of new photocell when covered and exposed to light (significant change - although couldn't find typical resistance for MZ 770 S). I have tried starting the boiler with photocell covered, photocell exposed to light, and normal with cell covered after ignition - in each case, it causes the boiler to lock out as expected.
Is the start up sequence:
Pump/motor and ignition transformer start together
Coil energised and oil valve opened
Photocell either senses flame or does not sense flame, leading to lockout
If so, my thinking is:
- no issue with oil supply (plenty of oil, new pump and motor working correctly, pump pressure set by engineer and same as when runs without lockout)
- issue seems to be either the oil valve not opening when energised or another fault causing oil valve not to open, leading to lock out as no flame established
- could it be another faulty new photocell (and is the photocell active prior to ignition?) Disconnecting photocell on next reset could rule this out if same problem experienced and boiler does not ignite?
- could it be faulty new coil/valve - and would it cause such an intermittent fault given new, fault occurs when coil 'cold'? But no problems with coil resistance, or operation of valve generally.
- could it be failing old ignition transformer (over five years old) - can this affect opening of valve/would it cause lockout so quickly?
- could it be failing old control box (over five years old) - do these tend to cause intermittent faults or just fail?
- could it be faulty electrical connections at control box, causing intermittent fault when cold? I can quickly check these with mains supply disconnected.
Not sure how best fault-finding process to take next to narrow down cause of fault, and avoid simply replacing parts.
I would welcome thoughts. Apologies for long post - don't want to waste your time so tried to provide all I know up front.
Thanks everyone.
I have a Danesmoor Utility 15/19 oil boiler with B9B burner and Satronic TF830.3 control box. Boiler sited indoors in upstairs room with outside tank lower than boiler, so Tigerloop fitted. Filter at tank and before boiler. Over 500l of oil in tank.
It had annual service in November - two visits, with changes made including:
Visit 1: new nozzle, tune up, clean and filter checks, new pump with coil, new motor (noisy bearings), new photocell (old one faulty)
Visit 2: new Tigerloop (old unit had failed with oil in upper chamber)
When the boiler runs, it runs very smoothly without problems, and can run for several hours. However, prior to the service, there was an intermittent lock out with the boiler locking out every other day - the engineer has tried to resolve this fault at each service visit in November, but the fault is now worse than before, with lock outs happening at least twice daily. The boiler is programmed to come on for periods of two hours in the early morning and early evening - typically it has locked out when period starts or on first start of programmed period.
Engineer not currently returning calls. Hoping to narrow down cause of fault to get heating running again before it gets colder.
If locked out and there is demand - I press reset on the control box, boiler motor and pump starts, ignition transformer can be heard (and flicker of sparks seen through peephole). Click of oil pump valve is not heard - but magnetic field detector held against coil very briefly lights (under a second) before boiler locks out. No evidence of oil in blast tube or nozzle tip
It typically restarts on second reset - same start up sequence, but click of solenoid valve heard (magnetic field detected and sustained, voltage pen senses increases in voltage from control box to solenoid), flame sustained.
Pump (BFP 21 L3) pressure starts at c100psi, tends to settle at around 92/94 psi with no obvious impact on operation - this is the same when it locks out as when it runs. A little foam in bottom chamber of Tigerloop on first start but reduces to none/very little on longer runs. Causes minor fluctuations in pressure reading but doesn't affect flame establishing/being sustained) and has run on this setup for many years.
I have checked resistance of solenoid coil (071N0810) across bottom two terminals (not open circuit hot or cold), and I have checked resistance of new photocell when covered and exposed to light (significant change - although couldn't find typical resistance for MZ 770 S). I have tried starting the boiler with photocell covered, photocell exposed to light, and normal with cell covered after ignition - in each case, it causes the boiler to lock out as expected.
Is the start up sequence:
Pump/motor and ignition transformer start together
Coil energised and oil valve opened
Photocell either senses flame or does not sense flame, leading to lockout
If so, my thinking is:
- no issue with oil supply (plenty of oil, new pump and motor working correctly, pump pressure set by engineer and same as when runs without lockout)
- issue seems to be either the oil valve not opening when energised or another fault causing oil valve not to open, leading to lock out as no flame established
- could it be another faulty new photocell (and is the photocell active prior to ignition?) Disconnecting photocell on next reset could rule this out if same problem experienced and boiler does not ignite?
- could it be faulty new coil/valve - and would it cause such an intermittent fault given new, fault occurs when coil 'cold'? But no problems with coil resistance, or operation of valve generally.
- could it be failing old ignition transformer (over five years old) - can this affect opening of valve/would it cause lockout so quickly?
- could it be failing old control box (over five years old) - do these tend to cause intermittent faults or just fail?
- could it be faulty electrical connections at control box, causing intermittent fault when cold? I can quickly check these with mains supply disconnected.
Not sure how best fault-finding process to take next to narrow down cause of fault, and avoid simply replacing parts.
I would welcome thoughts. Apologies for long post - don't want to waste your time so tried to provide all I know up front.