Hello folks,
My first post and I'm afraid it's a long one! I'm looking for some advice in an ongoing central heating problem I've been having since the start of December.
I've got a Y plan Honeywell central heating system which is about 18 years old. The system started out with a ST1591 programmer which allows HW, CH or a combination of both, a T6360B room thermostat in the living room, a L641A Cylinder thermostat and a V4973A motorised mid position valve.
I have a service contract with a Glasgow based healthcare company whom I will not name and I contact them at the start of December because we were having an intermittent fault where the boiler would not fire when the central heating was switched on, but would work fine when the hot water was switched on.
The company sent out engineer 1 who couldn't get the system to fault but suggested that as the boiler was working for hot water, the problem lay with either the room thermostat or the micro switch in the mid position valve (the micro switch was replaced about 2 years ago for a similar fault). However, as he couldn't get the system to fault he couldn't order any parts and suggested that the next time it happened, I should turn the room thermostat and if I heard an audible click, the problem was likely with the micro switch and I should contact the company so they could order the part. I duly did as asked, the thermostat did click so I passed on the information to the company.
A couple of days later, they contacted me to say that they wanted to send out an engineer to make sure they were ordering the correct part. I agreed to this and engineer 2 turned up. I was working, but my wife explained the problem to him, he looked at the system and suggested that the fault actually lay with the thermostat on the cylinder. My wife explained to him that the hot water was fine, but he insisted it was the cylinder thermostat and order a replacement.
Engineer 2 returned and replaced the thermostat, insisted the system was working because there was heat in the radiators (he had switched on both hot water and heating) and left. The next time we tried to switch on the heating, same fault.
Contacted the company again and they sent out Engineer 2. He looked again and decided that in fact, the whole mid position valve was faulty and needed replaced. The part was ordered and he eventually came round to fit it.
As mentioned above, the original valve was a Honeywell V4073A motorised mid position valve. The new valve is a Dayton ZA3 diverted valve. He drained down the system, replaced the valve, but then couldn't get the system to refill, blaming an air lock and blocked cold feed pipe. He said he didn't have the tools to unblock the feed pipe, so decided to backfill the system. After 3 failed attempts, he got the system back filled and left. We switched on the heating and nothing happened. We switched on the hot water and the radiators heated up to unbearably high temperatures but we had no hot water at all.
Called them back out, engineer 2 returned, drained the system, took the valve out, put it back in, messed about in the loft and then decided that the programmer was faulty. Said he'd order a new one and left.
That night, I noticed water coming through my living room ceiling. I drained the system, switched off the mains water and called them back out, only to be told there were no emergency engineers and I would need to phone again in the morning. Eventually, Engineer 3 arrived at 6pm the next night after I'd taken the day off work. He fixed the leak (Engineer 2 had left the safety valve on the pump open) and refilled the system. He then proceeded to get two electric shocks from the copper pipes. He took a quick look at the wire centre and reckoned it hadn't been wired correctly - the only change recently being the new valve. By this point it was 7:15pm and he couldn't stay any later (the poor guy had travelled quite a distance and mentioned he'd spent his whole day fixing engineer 2's mistakes). He recommended calling the company in the morning but that he system should remain off until it was checked.
I called the company back the next morning and they told me that the electric problem was a fault with my house and that I needed an electrician. I explained that their engineer had suggested that the wire centre was incorrectly wired and they agreed to send someone else out.
Engineer 2 was meant to come this morning but didn't show up, so after another irate phone call, they've agreed to send engineer 3 out on Wednesday.
Anyway, I have had a look around the forums and I have discovered that the Honeywell valve which was removed was a 5 wire mid position valve and the new valve is a 3 wire diverter valve. I think this might be the reason that the system isn't working properly, but I don't have a lot of knowledge in this area. If it is the case that the new actuator is the problem, would the whole valve need replaced, or could a Honeywell motor just be swapped in in place of the Dayton unit?
Any advise would be great fully received!
My first post and I'm afraid it's a long one! I'm looking for some advice in an ongoing central heating problem I've been having since the start of December.
I've got a Y plan Honeywell central heating system which is about 18 years old. The system started out with a ST1591 programmer which allows HW, CH or a combination of both, a T6360B room thermostat in the living room, a L641A Cylinder thermostat and a V4973A motorised mid position valve.
I have a service contract with a Glasgow based healthcare company whom I will not name and I contact them at the start of December because we were having an intermittent fault where the boiler would not fire when the central heating was switched on, but would work fine when the hot water was switched on.
The company sent out engineer 1 who couldn't get the system to fault but suggested that as the boiler was working for hot water, the problem lay with either the room thermostat or the micro switch in the mid position valve (the micro switch was replaced about 2 years ago for a similar fault). However, as he couldn't get the system to fault he couldn't order any parts and suggested that the next time it happened, I should turn the room thermostat and if I heard an audible click, the problem was likely with the micro switch and I should contact the company so they could order the part. I duly did as asked, the thermostat did click so I passed on the information to the company.
A couple of days later, they contacted me to say that they wanted to send out an engineer to make sure they were ordering the correct part. I agreed to this and engineer 2 turned up. I was working, but my wife explained the problem to him, he looked at the system and suggested that the fault actually lay with the thermostat on the cylinder. My wife explained to him that the hot water was fine, but he insisted it was the cylinder thermostat and order a replacement.
Engineer 2 returned and replaced the thermostat, insisted the system was working because there was heat in the radiators (he had switched on both hot water and heating) and left. The next time we tried to switch on the heating, same fault.
Contacted the company again and they sent out Engineer 2. He looked again and decided that in fact, the whole mid position valve was faulty and needed replaced. The part was ordered and he eventually came round to fit it.
As mentioned above, the original valve was a Honeywell V4073A motorised mid position valve. The new valve is a Dayton ZA3 diverted valve. He drained down the system, replaced the valve, but then couldn't get the system to refill, blaming an air lock and blocked cold feed pipe. He said he didn't have the tools to unblock the feed pipe, so decided to backfill the system. After 3 failed attempts, he got the system back filled and left. We switched on the heating and nothing happened. We switched on the hot water and the radiators heated up to unbearably high temperatures but we had no hot water at all.
Called them back out, engineer 2 returned, drained the system, took the valve out, put it back in, messed about in the loft and then decided that the programmer was faulty. Said he'd order a new one and left.
That night, I noticed water coming through my living room ceiling. I drained the system, switched off the mains water and called them back out, only to be told there were no emergency engineers and I would need to phone again in the morning. Eventually, Engineer 3 arrived at 6pm the next night after I'd taken the day off work. He fixed the leak (Engineer 2 had left the safety valve on the pump open) and refilled the system. He then proceeded to get two electric shocks from the copper pipes. He took a quick look at the wire centre and reckoned it hadn't been wired correctly - the only change recently being the new valve. By this point it was 7:15pm and he couldn't stay any later (the poor guy had travelled quite a distance and mentioned he'd spent his whole day fixing engineer 2's mistakes). He recommended calling the company in the morning but that he system should remain off until it was checked.
I called the company back the next morning and they told me that the electric problem was a fault with my house and that I needed an electrician. I explained that their engineer had suggested that the wire centre was incorrectly wired and they agreed to send someone else out.
Engineer 2 was meant to come this morning but didn't show up, so after another irate phone call, they've agreed to send engineer 3 out on Wednesday.
Anyway, I have had a look around the forums and I have discovered that the Honeywell valve which was removed was a 5 wire mid position valve and the new valve is a 3 wire diverter valve. I think this might be the reason that the system isn't working properly, but I don't have a lot of knowledge in this area. If it is the case that the new actuator is the problem, would the whole valve need replaced, or could a Honeywell motor just be swapped in in place of the Dayton unit?
Any advise would be great fully received!