My house has (all installed prior to my ownership) a brick outbuilding.
There is an SWA cable feeding the outbuilding via a 16A MCB in the main consumer unit within the house protected by a 30mA RCD.
Within the outbuilding there is a small consumer unit with a 30mA RCD, a 6A MCB feeding some lights and a couple of 16A MCBs feeding some 13A sockets and also a heater in a greenhouse which is attached. All the wiring is a bit of a mess and I'm planning to refit it all at some point. I don't need anything particularly elaborate, probably a couple of twin 13A sockets, an external 13A socket, and a light.
What I'm pondering is; is there any need for the CU in the outbuilding? Given the feed is protected by both a 16A MCB and a 30mA RCD anyway, does the second CU add anything? I'll probably keep it anyway given it's already there and it provides a good enclosure to house all the cabling rather than cramming it all into socket backboxes, but it strikes me the whole lot could simply be wired as a radial circuit, subject to using an FCU instead of a light switch to provide appropriate protection for the lighting?
Alternatively, would it be a better idea to wire the SWA from a non-RCD protected MCB in the house consumer unit, thus removing the possibility of nuisance tripping the house circuits as a result of issues outside, and instead rely on the external RCD?
What would be the normal / recommended way of connecting such an arrangement?
There is an SWA cable feeding the outbuilding via a 16A MCB in the main consumer unit within the house protected by a 30mA RCD.
Within the outbuilding there is a small consumer unit with a 30mA RCD, a 6A MCB feeding some lights and a couple of 16A MCBs feeding some 13A sockets and also a heater in a greenhouse which is attached. All the wiring is a bit of a mess and I'm planning to refit it all at some point. I don't need anything particularly elaborate, probably a couple of twin 13A sockets, an external 13A socket, and a light.
What I'm pondering is; is there any need for the CU in the outbuilding? Given the feed is protected by both a 16A MCB and a 30mA RCD anyway, does the second CU add anything? I'll probably keep it anyway given it's already there and it provides a good enclosure to house all the cabling rather than cramming it all into socket backboxes, but it strikes me the whole lot could simply be wired as a radial circuit, subject to using an FCU instead of a light switch to provide appropriate protection for the lighting?
Alternatively, would it be a better idea to wire the SWA from a non-RCD protected MCB in the house consumer unit, thus removing the possibility of nuisance tripping the house circuits as a result of issues outside, and instead rely on the external RCD?
What would be the normal / recommended way of connecting such an arrangement?
Last edited: