Well, never mind the FCUs, why have you decided to run 10 circuits in 2.5 off a 32A fuse?
Ring or radial on a 2.5 T&E on a 32A OPD is not uncommon.
With a ring we might have a number of spurs (common example being a number of points (sockets say) and from each of those points we might have a radial consisting of one end point each, again in 2.5 T&E, all allowed and nobody seems alarmed by any potential problems.
So far so good?
We might run a radial of 2.5 T&E on a 16A or 20A MCB and we might even run a spur from each point on the radial consisting of one point only on each spur.
We might at some points branch off and branch off and branch off in a design known as "trees" .
Mightbe a beggar to inspect and test and then write down the result but heyho its allowed.
So far so good?
We might have ten or more or less radials each connecting to one fuseway at one end and each connecting to one point only at the other end, once again all cables are 2,5 T&E.
We might decide that it does not comply with BS7671 but some might decide that it does.
However, is it potentially any less safe than the examples above?
So far so good?
We might have a radial circuit of 4.0 T&E or even 6.0 T&E if the terminals on the points accept those whilst still being electrically and mechnically sound and we might similarly run a 2.5 spur to a point on each one.
Some of those might be considered as "standard circuits" whilst some might not.
Is something not easily recognised as a standard circuit still allowed by BS7671? Yes.
Could something not complying with BS7671 be potentially unsafe? It might be or it might not..
Is something not as easy to test and inspect to BS7671 still permitted? Yes.
So far so good?
The over riding aim is safety of people, livestock and property!
So far so good?
Anyway i have not decided to run 10 circuits in 2.5 T&E on a 32A fuse (or breaker) and I never would. But what if I did? Would it be unsafe?