Outside socket protection

Joined
10 Feb 2017
Messages
126
Reaction score
4
Location
Newport Wales
Country
United Kingdom
Hi
Recently bought a house
It has an outside socket in front garden for lawnmower etc. this is fed by Time guard RCD Spur Double Pole.
The RCD Spur is faulty and doesn’t work.
The house recently had a new consumer unit installed with integral RDD etc.
QUESTION do I need to fit another RCD Spur or would a fused DP Isolator suffice?
Thanks
 
Sponsored Links
If the circuit is RCD protected at the consumer unit ,you don't need another RCD. A double pole isolation switch is a good idea. A fuse may or may not be needed.
Please give details of the circuit OPD ,and cable size to the outside socket.
 
Sponsored Links
The isolator does not need to be fused. Your lawn mower (or whatever) already has a fuse.
 
I think the point Terry was making is that the isolator MAY have to be fused.
 
The Timeguard unit was fused, so I took the belt and braces view.
The difference in cost between fused or not is less than a £1
 
I’m not without some common sense gents.
Cable is 2.5 t and e
It’s on its own mcb and the consumer unit is RCD protected

I checked all that before I asked. The origiginal RCD Spur device was left over from an earlier install

I’m happy to fit a double pole fused switch
 
The Timeguard unit was fused, so I took the belt and braces view.
The difference in cost between fused or not is less than a £1
But it is not belt and braces. If there is a fault you will have two fuses blow, the unnecessary one and the one in the plug.
 