Circuits aren't 'fed'; the loads 'draw' current.Even though the plug fuse is after the 2.5mm cable? The way I imagine this circuit is the 2.5mm cable has nothing before it down-rating the 32a circuit. In other words it is being 'fed' by a 32a MCB.
I'll say "No" but am not sure what it means.MCB's aren't self negotiating, are they?
The circuit is not 'delivering' anything.So take a simple circuit of MCB > cable > FCU > appliance, even though you might have a 3a Fuse in the FCU, the circuit is delivering 32a up to the FCU? After that it's 3a so can use 1mm cable.
The current 'drawn' is dependent upon the load and the characteristics of this load mean that various means can be implemented to ensure it is safe.
I didn't, however...Not sure if you saw my edit before posting?