How do you know that is not on the cooker circuit - as it should be?The is some sort of plastic cover with wires on the wall where the oven will go. I know it needs to be hard wired in. I think we will need to run a new 6mm cable and create new circuit for just the oven.
Ok, fair enough.I will ask him when he is back from holiday. I assume the hob is separate to oven because it has a separate mcb on consumer unit. If I turn off the fuse for oven, the 3 appliances is also turned off.
Assuming this is a ring circuit with the 32A MCB which you have told us.Hope someone can help advise if this ok. Electrician has wired 2.5mm circuit
Not really - or rather - No.for oven, washing machine, tumble dryer and dishwasher. I just bought an double oven that is 5.1kw. Is it ok to have this on a 2.5mm circuit with the other appliances?
It would still be pushing your luck and it would not be the oven you want.If not, what is the best option?
1) change to smaller oven (what is the maximum kw I can have?)
You could do that - but if it is that easy to rewire then just connect the oven to the hob circuit and leave the rest as is.2) put the appliances on circuit with the other sockets
No point. All you need is a cable - 2.5mm² would do but I would use 4mm² - from the hob connection point to the oven.3) change cable to 6mm (which be a pain to do and no doubt cost more). Can the appliances be kept on the same circuit with 2.5mm cable?
Isn’t it best to have hob on its own circuit? This seems to be the common recommendation that I read about on the internet. Along with future proofing using 6mm cable instead of 4mm.You could do that - but if it is that easy to rewire then just connect the oven to the hob circuit and leave the rest as is.
I do not understand why that was not the original way of doing it.
Electrically it makes no difference.Isn’t it best to have hob on its own circuit?
Everything on the internet is right.This seems to be the common recommendation that I read about on the internet.
You had better rewire everything with 6mm², then.Along with future proofing using 6mm cable instead of 4mm.
We did not know that.I don’t think we can connect the oven to hob circuit as the hob is on island and I guess you can’t do this without breaking the floor tiles.
Glad to hear it.Everything on the internet is right.
I will tell the electrician your recommendation.You had better rewire everything with 6mm², then.
Entirely your fault then...Partly my fault as I gave him the impression I was getting a less powerful oven.
Glad to hear it.
I will tell the electrician your recommendation.
Having read a lot of posts on this forum 2 nights ago, I did get the impression that he knows his stuff.he is normally bang on the money with his advice.
Says 40A on the MCBneed to know the size of MCB protecting the circuit that the hob is on.
Tell that to the so called electrician who stuck a plug on a 2.5mm cable and plugged it into a Double socket under an island unit on a 32amp ring final for the HobAre you sure the oven is on this new ring? How is it connected?
You can't plug in a 5.1kW oven.