Sorry iof it wasn't clear. It was really the first sentence/paragraph which mattered - and I was agree with endecotp that I have never personally been aware an RCD or RCBO intended for use in a CU whose test button created a simulated 'fault' to earth (even in the case of RCBOs which have a functional earth connection). If the test button does not simulate a fault to earth but, rather (as has every one I've been aware of) sends a small current from L on one side of the RCD/RCBO to N on the other side (thereby creating a current imbalance which trips the device), then it would not cause an upstream RCD to trip.John, Really sorry have read your post several times but cannot quite understand what it is your saying
Had a choice of 2 1ph sub-main DBs, 1 was old MEM,
I'm not sure that I fully understand, but ....Can you not take your supply from this ?
MEM board was a non starter due to parts unavailable, and building owner said no to changing the DB.
find breakers for the old memshield DB. Think it was memshield 2. If I could have found at breaker to fit then it was always to be my preferred choice as it would have eliminated the Rcd in series problem.
Could not find memsheild 63a, or find compatible components
Indeed - but even if they were of different (trip current) ratings, there would be no guarantee that the lower-rated one would trip first. Don't forget that a fault current could be considerably in excess of the trip threshold of either of them2 rcds (or RCBOs) at the same rating is not the best. My understanding, pressing the test button on an RCD or RCBO in a DB downstream (the end) when the RCD/RCBO has the same rating as the RCD upstream (Source) can cause either RCD to see the fault and trip. This I already new but hoped would not happen if honest.
I'm not convinced that, regulations-wise, it would make any difference. Forgetting the issue of what happens when you press test buttons, in either case a fault on any of the circuits from the new CU could take out the upstream Hager's RCD and hence everything else protected by that RCD. Whether it would or would not be compliant with current regulations would depend upon whether you (or whoever) felt that reasonable steps had been taken to "minimise inconvenience" (due to multiple circuits being killed) in the event of a single fault.Just to confirm current 17th regs, I assume the easiest fix at this time is to remove all RCBOs in new board and replace with MCBs, thus retaining the RCD protection from the 63A 30mA RCD on the upstream Hager board