On a slightly related topic, I noticed that the location field has been updated to include England, Wales, Ireland and Scotland. Unfortunately, when I tried changing mine to Wales after I click 'submit' it reverts back to UK.
I don't treat England as being the entire UK, I just can't be bothered to keep asking people who post in "Electrics UK" if they live inside or outside England and Wales.JohnD said:many citizens of the UK who live in, or come from, parts of the UK which are not England, are very offended by the lazy mind which treats "UK" as equivalent to "England".
So let me get this straight.notyou said:As far as part p goes there is formal arrangement or indeed any requirement in any electrical installation test part p or not for load currents to be measured if a item is ce marked and duly rated.
I don't think 1.2 is the right correction factor for rewireable fuses - where did you get that from?The reason as to my uncertainty over the white one way wylex is that it is not ce marked and labelled.
To replace a cable that is burnt out and cut is a replacement again not part p, altering the characteristics of a cable by changing a bs3036 re wirable fuse of 30amp to 60898 mcb rated at 45 amp does 2 things firstly negates the need to de rate the ccc by 1.2 of load current and actually comply with regs with regard to load current being smaller than the protective devices.
Er, eh?THus making everything much safer!
I've never changed the shower its always been on the wall, how can you replace a cable without connecting it to something, and then claim it has to be part p.
Clearly. I can hardly believe you have to ask.Or would you expect to put a couple of joint boxes in instead and wire in new bit of cable. surely it is safer to have te cable replaced instead of a jointed repair!
notyou said:4 what is your straight question?
I said:Also, have you confirmed that this MCB is supplying only the shower?
I also said:Are you absolutely sure that the shower rating is 9.5kW?
And I also said:is it in any way possible that the shower has been fitted with a 10.5kW can? Did you buy the shower? Was it in the house already? Has anyone ever 'mended' it?
Softus said:I'm all for some blind spurting.
That's somewhat debatable, since this discussion is routine on the "Electrics UK" forum.empip said:Here lies a strange situation :-