That's not what you said earlier. You were claiming that "fused spur" is synonymous with "fused connection unit." You've also claimed that a fused spur ends at the FCU, implying that the feeder cable is part of the fused spur but not any cable downstream of the FCU.
Just what exactly do you think that the term "fused spur" includes?
[code:1]Socket ≡ socket. The exemption for "work which consists of adding a socket" necessarily includes exemption
for the cables, clips, box, junction boxes, crimps, blanking plates, conduit, trunking
capping etc which are an integral part of it.
Switch ≡ switch. The exemption for "work which consists of adding a switch" necessarily includes exemption
Light ≡ light. The exemption for "work which consists of adding a light" necessarily includes exemption
Fused ≡ FCU. The exemption for "work which consists of adding a fused spur" necessarily includes exemption
spur for the cables, clips, box, junction boxes, crimps, blanking plates, conduit, trunking
capping etc which are an integral part of it. [/code:1]
Yes, with either your interpretation or mine the result is a whole host of inconsistencies.
Show me mine. Specifically show me any which mine actually
create.
You seem to be trying to read things into schedule 4 which aren't written there just to remove a few of them.
Such as?
Just because one interpretation of the regulations results in more inconsistencies does not necessarily mean that the interpretation is incorrect.
Not only is it incorrect, it is incorrect to the point of utterly perverse lunacy to deliberately seek to create inconsistencies.
The law is full of inconsistencies.
I'm concerned purely with the few lines which make up Schedule 4.
Saying that the cable is part of the socket and saying that the cable is a necessary part of work which consists of adding a socket are not the exactly same thing.
Within the context of what activities Schedule 4 exempt from notification it is.
Adding the cable is not part of adding the socket itself, but it is part of the work which consists of adding the socket. There's a subtle difference.
No there isn't.
So if you were adding a fused spur to feed a new socket, fitting the FCU to make the spur fused would also be part of your "atomic" work of a single, complete process.
If you decided that it was sensible to class a functioning device with protective device selection aspects as nothing more significant than a piece of choc-block.
But according to you, without the reference to a fused spur in 2(c)(ii), that would be notifiable because of the new FCU.
I find it hard to class a functioning device with protective device selection aspects as nothing more significant than a piece of choc-block.
We are dealing with what Schedule 4
is, and to see whether the way that it
is works, which it does, 100% by treating "fused spur" the way I say.
One could speculate on how it would work were it worded differently, but even if we agreed with your assertion that adding a fused spur when adding a socket could be defined to be an integral part of the socket, thus we could easily remove the explicit reference to fused spurs, we are then,
according to you, left with:
what would happen if all you wanted to do was to add an FCU - no other work of which it could be an incidental part, e.g. if you found an unfused spur with more than one socket on, and so you wanted to add an FCU before the sockets?
Then it would become notifiable.
It seems a bit rich for you to object to me saying the same as you.
But that's what you're doing with your interpretation that adding a fused spur for a socket would be notifiable but for the reference to "fused spur" in 2(c)(ii). The FCU would be a necessary part of the task of adding a socket on a fused spur, just as the cable is a necessary part of adding the socket on a fused or a non-fused spur. As you've just said, you can't have it both ways.
I don't want it both ways - I'm dealing with Schedule 4
as it is, not deciding that I don't want it to be as it is, and therefore rejecting definitions so that I can claim that it is faulty and thus claim legitimacy for proposing that it should be written differently, with more and more changes needed to resolve inconsistencies I keep creating.
I don't regard FCUs as trivial as a bit of choc-block, and neither does Schedule 4.
Given
the fact of how Schedule 4 is, my explanation of what a fused spur is makes it all work perfectly well.
Your rejection of my explanation, and your suggested alternative of how Schedule 4 might be
creates the problem of an FCU on its own becoming notifiable thanks to your removal of its exemption.
You said so yourself.
That is exactly my point with regard to your interpretation that fitting an FCU to add a socket on a fused spur would be notifiable but for the reference to a fused spur in 2(c)(ii).
Either:
(a) the ancillary items necessary to carry out the single task of adding a socket are implicitly exempt as "work which consists of adding a socket," and that would include both the cable and the FCU, or
(b) you would need to find an explicit reference which exempts both the cable and the FCU.
Which of those options would you like?
For your interpretation (b) regarding the FCU, you would then be left with the consequence that installing a socket on a non-fused spur would also be notifiable, because there's no explicit exemption for cable.
I wouldn't have any such problem at all, because I'm not tampering with the way that Schedule 4 is - I'm leaving the explicit mention of fused spur in there, which means I don't have to try and make it part of adding something else and I don't have to resolve a problem entirely created by you suggesting that the explicit mention of a fused spur be removed and simultaneously saying that I'd end up with a problem because your removal contradicted my position.
You can't challenge my position regarding Schedule 4
as it is by saying that it becomes invalid when applied to an alternative version of Schedule 4 which you've decided to create.
If you want the cable to be implicitly exempt, then you have to go with (a), which would also make the FCU implicitly exempt as a necessary part of the overall task of adding the socket.
I don't have to do anything of the sort because FCUs don't require an implicit exemption - they
already have an explicit one in Schedule 4.
But you don't think that adding an FCU to install a socket on a fused spur would be an integral part of that task. You're introducing one of those inconsistencies which you dislike.
No I'm not.
I'm dealing with Schedule 4 as it is.
If you want to add a socket on a fused spur where is the inconsistency in the socket being exempt and the fused spur being exempt?
What doesn't work because fused spurs are explicitly mentioned?
That's what I said. They're an integral part of the work which consists of adding the socket, not an integral part of the socket itself.
Fine - then read Schedule 4 more precisely.
It's not the socket which is exempt from notification, it's the work which consists of adding the socket. If you want the exemption to apply to the actual adding of just the socket itself during that work then it has to apply equally to the actual adding of the cable.
But the location of a fused spur is not so simple when part of it is in a kitchen and part is not.
It is when you say that fused spur ≡‎ FCU.
Again I am offering you a definition which simplifies and which creates no inconsistencies and again you reject it purely because you don't like the word they used, and you persist in that rejection despite all of the problems which arise.
A socket is in one particular place. Arguments over the boundaries of an open-plan layout aside, either it's in the kitchen or it isn't.
Ditto for FCU.
But a fused spur can encompass an area in the kitchen and an area outside it.
An FCU cannot.
A socket is just a socket, and the cable is incidental in terms of being a necessary part of work consisting of adding the socket.
An FCU is just an FCU, and the cable is incidental in terms of being a necessary part of work consisting of adding the FCU.
An fused spur is just a fused spur, and the cable is incidental in terms of being a necessary part of work consisting of adding the fused spur.
The cable is not just such an incidental part though, it is an integral part of the collection of items which comprise a fused spur.
It is no more or less incidental than the cables for a socket.
You could install a socket with no cables. It would do SFA, but it would still be a socket. Because of the pointlessness of that it's obvious that the action labelled as "work which consists of adding a socket" encompasses the addition of all the necessary materials integral to adding a socket.
You could install an FCU with no cables. It would do SFA, but it would still be an FCU. Because of the pointlessness of that it's obvious that the action labelled as "work which consists of adding a fused spur" encompasses the addition of all the necessary materials integral to adding an FCU.
As such, a fused spur may be part in a kitchen and part outside it. Why, when a fused spur comprises both the FCU and associated cables, should its official location then be determined solely by the location of the FCU?
For exactly the same reason that when "work which consists of adding a socket" is examined for notifiability it is the location of the socket which is relevant, not the location of the associated cables.
Again we come back to a simple question: If the intent was that the FCU itself were accorded some special status in its own right, as in determining whether or not a fused spur is deemed to be within a kitchen or not, then why do the regulations not simply refer to a fused connection unit instead of a fused spur?
I don't know why they used that term.
All along I've taken your suggested alternative meanings, and suggested alternative wordings, and said "OK - if you're right what about.....".
Do me the same courtesy.
Schedule 4 can be regarded as a process which you run to produce a result, that result being a determination of whether the work you want to do is exempt.
What wouldn't work if Schedule 4 was worded like this: (non-electrical parts removed for clarity)
[code:1]1. Work consisting of -
(a) replacing any fixed electrical equipment which does not include the provision of -
(i) any new fixed cabling, or
(ii) a consumer unit;
(b) replacing a damaged cable for a single circuit only;
(c) re-fixing or replacing enclosures of existing installation components, where the circuit
protective measures are unaffected;
(d) providing mechanical protection to an existing fixed installation, where the circuit
protective measures and current carrying capacity of conductors are unaffected by the
increased thermal insulation;
(e) installing or upgrading main or supplementary equipotential bonding;
2. Work which -
(a) is not in a kitchen, or a special location;
(b) does not involve work on a special installation; and
(c) consists of -
(i) adding light fittings and switches to an existing circuit, or
(ii) adding socket outlets and FCUs to an existing ring or radial circuit.
3. Work on -
(a) telephone wiring or extra-low voltage wiring for the purposes of communications,
information technology, signalling, control and similar purposes, where the wiring is
not in a special location;
(b) equipment associated with the wiring referred to in sub-paragraph (a);
(c) pre-fabricated equipment sets and associated flexible leads with integral plug and
socket connections.
4. For the purposes of this Schedule -
"kitchen" means a room or part of a room which contains a sink and food preparation
facilities;
"self-contained" in relation to a fixed building service means consisting of a single appliance
and any associated controls which is neither connected to, nor forms part of, any other fixed
building service;
"special installation" means an electric floor or ceiling heating system, an outdoor lighting or
electric power installation, an electricity generator, or an extra-low voltage lighting system
which is not a pre-assembled lighting set bearing the CE marking referred to in regulation 9 of
the Electrical Equipment (Safety) Regulations 1994(a);
"special location" means a location within the limits of the relevant zones specified for a bath,
a shower, a swimming or paddling pool or a hot air sauna in the Wiring Regulations,
seventeenth edition, published by the Institution of Electrical Engineers and the British
Standards Institution as BS 7671: 2008(b).[/code:1]
So you think that for legal purposes we can simply choose to redefine what a term means in legislation if it removes an inconsistency?
I'm not redefining anything - there is (despite what Stoday says) a huge amount of precedent of people using the term "fused spur" to mean FCU, and it is a perfectly realistic scenario, given that the legislation was instigated and defined by people who were, or had been, actual electricians rather than scientists, that when they asked the civil servants to add "fused spur" to the list of "lights, switches and sockets" they did indeed mean FCU.
And using that definition does make Schedule 4 work without any problems at all.
I'm not trying to get it to exempt any more or less at all, merely pointing out how it can be interpreted.
All of your interpretations lead to having to make changes to it to make it work, mine does not.
What would be any ulterior motive anyway? I've been against the entire mess of Part P from its inception, and as far as I'm concerned no electrical work in one's own home should be notifiable.
That may well be the case, but it would be reprehensible in the extreme for you to allow that to colour your judgement when it comes to dealing with Schedule 4
as it is.
This whole thing started, remember, because you were trying to find a way to declare the addition of new smoke alarms, i.e. new fixed electrical equipment, to be non-notifiable despite Schedule 4
as it is not doing that.
The law is pedantic over such "semantic inexactitudes."
OK - fine.
I'm just as happy with saying that "adding light fittings and switches to an existing circuit, or adding socket outlets and fused spurs to an existing ring or radial circuit means adding any or all of those as I am with saying that "fused spur" means FCU.
But if you believe that the way Schedule 4(2) is written has to be taken exactly as it is if we can't proceed with it as if it were written differently, then I look forward to you informing people that they can't add just a light or just a switch - they have to add both for it to be non-notifiable, and that they can't add just a socket outlet or just a fused spur, it has to be both.
But "fused spur" does not mean just an FCU, as has been pointed out numerous times already.
I say it does, and saying that makes sense, is justifiable in terms of usage and is justifiable in terms of the operation of Schedule 4.
Why do you want to try and redefine "fused spur" to mean just an FCU when a fused spur, by definition, already includes the cables?
I'm not redefining it - I'm saying that's what it means. I'm changing nothing - I maintain that it has always meant that.
Yes, functionally it's almost the same. But if a fused spur does not extend beyond the FCU as you have claimed, where is the exemption in schedule 4 for fitting either one?
The same place as the exemption for fitting a junction box as an integral part of work which consists of adding a socket.
Of course the cable supplying the socket can be an integral part of the work which consists of adding the socket. But that doesn't stop it from also being a part of the fused spur.
As "fused spur" ≡‎ FCU then the cable is not "part of the fused spur" it's an integral part of the work which consists of adding the fused spur.
"fused spur" ≡‎ FCU may offend you with it's terminological inexactitude but it doesn't break the working of Schedule 4, it doesn't create inconsistencies with the say Schedule 4 describes and deals with sockets, switches and lights, it doesn't introduce any discrepancies with the way to deal with junction boxes and other ancillary items when used with fused spurs/sockets/lights/switches and it is not inconsistent with respect to what we know the intention of bringing electrical work within the scope of the Building Regulations was.
But you've said that the fused spur doesn't extend beyond the FCU.
"fused spur" ≡‎ FCU.
Can an FCU extend beyond an FCU?
Can a socket extend beyond a socket?
How can the cable and outlet box then be part of the work consisting of adding a fused spur, if the fused spur ends at the FCU as you have claimed?
In the same way that the cables are part of the work of adding a socket.
"Socket" consists of a socket supplied by cables.
"Fused spur" ≡‎ FCU.
"Fused spur" consists of a fused spur supplied by cables.
FCU consists of an FCU supplied by cables.
All of them "stop" at the point of the socket/light/switch/fused spur aka FCU, but all of them when considering "work consisting of..." incorporate the necessary addition of cables, boxes, clips, conduit, junction boxes, flex outlet plates aka junction boxes, trunking, capping, crimps, sleeving etc etc etc which are integral to the installation of the /light/switch/fused spur aka FCU.
With fused spurs aka FCUs there's no problem with designating a load cable and flex outlet plate as an integral part of what you install when installing a fused spur aka FCU.
There
is a problem with saying that equipment supplied by the fused spur aka FCU is an integral part of what you install when installing a fused spur aka FCU, and that's what I meant - you were still trying to incorporate equipment supplied by a fused spur aka FCU into the fused spur aka FCU in order to make the installation of the equipment exempt via the exemption for fused spurs aka FCUs.
Yes, the provision of a new junction box which relates to any "work consisting of" which is exempted by schedule 4. So it could be a junction box used to tap into an existing circuit to spur off for a new socket or light under 2(c), or it could be a junction box (including a flex outlet type) added while replacing some equipment under the exemption in 1(a).
So in those situations it would be just as implicitly exempt as the cables, boxes, sleeving, crimps, capping, conduit, trunking etc etc.
The mere fact that the list of notifiable vs. non-notifiable jobs is vague and open to interpretation in some respects shows how badly written the regulations are.
It isn't vague etc, unless you reject the reasonable and explicable meaning of "fused spur".
It may very well
describe a regime which you don't think should exist, or it may well
describe a regime which you think is inconsistent (e.g. the kitchen/utility room nonsense), but that does not mean that
the way it describes that regime is faulty within itself.
The Approved Document is supposed provided guidance on these issues, so if somebody followed the advice offered in that officially issued document, is it likely that it would be queried, even if it is wrong, as has been claimed here?
That the AD clearly contradicts [the law] means that in practice nobody would ever get done for following the AD, but it does not mean that the AD is right and what it says in the law is wrong.