Once again I see people applying diversity on a circuit where it should not, and does not apply.
Diversity has a role to play in most electrical installations and certainly the majority of circuits, however circuits that supply fixed equipment should not have diversity applied.
A cooker may only be 80% used at any one time for the vast bulk of it's life, but there are occasions, especially in family homes, where the full potential load of the cooker may be used, such as at Christmas etc.
Please do not forget that cookers are NOT seperate circuits, they are a single piece of FIXED EQUIPMENT connected permanently to a single dedicated circuit.
This circuit should be capable of safely delivering the full potential load of that euipment should it be required, whether it is used as a rule or not.
6.1kW is 26.5A, and so the cooker in this case, should be connected to a Radial of not less than 4.0mm and protected by a 32A Type B MCB, preferably s 30mA 32A RCBO for added safety.
Diversity has a role to play in most electrical installations and certainly the majority of circuits, however circuits that supply fixed equipment should not have diversity applied.
A cooker may only be 80% used at any one time for the vast bulk of it's life, but there are occasions, especially in family homes, where the full potential load of the cooker may be used, such as at Christmas etc.
Please do not forget that cookers are NOT seperate circuits, they are a single piece of FIXED EQUIPMENT connected permanently to a single dedicated circuit.
This circuit should be capable of safely delivering the full potential load of that euipment should it be required, whether it is used as a rule or not.
6.1kW is 26.5A, and so the cooker in this case, should be connected to a Radial of not less than 4.0mm and protected by a 32A Type B MCB, preferably s 30mA 32A RCBO for added safety.