Also whats with the yellow with a bit of g/y tape on it, is that being used as an earth wire? As far as having poke-able live bits -that was the main issue with last week's wasn't it? (although in this one they look a lot less poke-able*)
Yes, lack of correct sleeving (and g/y it seems)!
The thing is, once a cover is removed from a consumer unit or distribution board you must expect to be met with live parts if you choose not to isolate the supply to it.
By not isolating the supply before removal of covers you're in breech of the Electricity At Work Regulations, a statutory document.
Work on or near live conductors
14. No person shall be engaged in any work activity on or so near any live conductor (other than one suitably covered with insulating material so as to prevent danger) that danger may arise unless-
(a) it is unreasonable in all the circumstances for it to be dead; and
(b) it is reasonable in all the circumstances for him to be at work on or near it while it is live; and
(c) suitable precautions (including where necessary the provision of suitable protective equipment) are taken to prevent injury.