Vapour membrane suggests a 'breathable layer between the old solid wall and the insulation. Im not sure what this would achieve?
In a timber frame construction a breathable membrane inside the ventilated cavity protects the timber frame from condensation. It's reasonable to assume if an insulated plasterboard manufacturer doesn't specify this it isn't required to protect their product.
How could condensation occur? - Lot's of factors in play including temperature, humidity, thermal capacity, and thermal inertia. In most circumstances a ventilated cavity will have air, which isn't saturated, moving across internal surfaces. Any internal dampness caused by either penetration or condensation will be "collected" by this non-saturated air as it tends to try and achieve moisture equilibrium, and the fact that it is moving (hopefully) means that it can be both extracted and replenished.
However, there are circumstances where the process can be reversed. If we have a long cold spell, the external brick skin becomes cold, and the internal face of the insulated skin is also cold. Both brick and insulation have a fairly high thermal capacity and slow thermal inertia. If the weather changes to warm and raining, the external air becomes saturated and at a higher temperature than the building fabric. because of thermal inertia it may well not warm up as rapidly as the changes in external air temperature and humidity, and hence condensation will occur. Now the ventilated cavity is introducing moisture during the period when these circumstances occur. It is this condensation that the breathable membrane counteracts by protecting the timber frame.
Fortunately, the building is generally warmer than the external air, so in most circumstances the air in the cavity will not be saturated, and evaporation not condensation will occur.
It is impossible to completely avoid condensation because external weather conditions in relation to internal temperatures and humidities can change rapidly, and insulation, by definition increases thermal inertia by slowing down heat energy transfer. This is why, in modern building designs ventilated spaces in walls and roofs is critical; by increasing the potential for condensation, we have to introduce robust methods of ensuring we can evaporate that condensation and extract it, or it will build up causing persistent damp problems.
IMO this is a very important observation in the guidance document linked:-
"
The lowest risk designs for internal wall insulation are consistent with the
existing moisture strategy of the building. For solid walled (traditional)
buildings, this is likely to be moisture open, so capillary active insulations
(such as woodfibre) and vapour open adhesives and finishes shall be chosen.
This does not involve the use of vapour barriers, but will include an air
barrier. This allows drying to both sides of the internal wall insulation and
therefore maintaining the moisture balance within the wall. A Bristolian’s
Guide to Solid Wall insulation contains more information about this approach
and illustrates a series of vapour open designs for internal wall insulation."
This is an alternative approach to a ventilated cavity in a solid wall building, because it does not rely on ventilation to extract moisture within the building fabric, but allows it to evaporate both internally and externally using moisture-open insulation and finishes. However, this
cannot be achieved using insulated plasterboard with PIR, EPS or XPS insulation which are "moisture closed" insulation materials relying on moisture and air barriers, and hence when these are used:- (point 45)
"
alternatively a moisture closed system with a ventilated cavity (of at least 25mm) on the cold side. "
...so, in my view the choice when internally insulating solid wall is either moisture open materials and no cavity allowing full "breathability", or a ventilated cavity on the basis that at some point internal condensation will occur and it has to be evaporated and extracted.
The challenge is we try and convert old buildings which were designed for minimal heating and lots of ventilation (open fires causing air replenishment, chimneys, and not-too-sealed windows) into buildings we want to perform like new-build with air-sealing and insulation to retain heat energy, sealed windows, hotter rooms etc. The original building fabric wasn't designed for this, and so conversion is challenging.
I have my opinions, which I have used practically in my own projects with, I believe, a good degree of success. I know people have different opinions, and undoubtedly the solutions are not perfect, because what may be a benefit in some circumstances can be detrimental in others. The best advice I can give is try and understand the science, and make your own decisions. FWIW I think the guidance on heritage-house is really good and also the gov. guidance I linked - both these sources seem to cut through the witch-doctory approach of the "damp" industry.
My final 2p on this thread