Hi I've been reading here for a few months and for my first post I was hoping someone could double check that I'm on the right track with my kitchen rewiring plan. First off I know it's part p and notice has been given to building control.
My house seems to have had a recent rewire and I have a new looking mem 2000AD CU.
1. HOB WIRING
I have a 6400w rated hob and there is already a cooker point wired with 4mm cable on a 32A breaker. I would like to reroute this cable without changing the length or extending it to run the hob and hob alone. Do I run the cable into an isolating switch 1st and then run some more 4mm to a hardwired cooker outlet? Is this all sufficient and in line with regs? User guide says 2.5mm and 25A so I presume this is ok for now but may not be adequate for an upgraded hob?
2. IMMERSION OUT BOILER IN
I have removed an old back boiler and am having a combi condensing boiler fitted. The old immersion (which has since taken a trip the scrap yard) was connected to a 16A breaker on 2.5mm cable. I would like to reroute this cable to run just the boiler. Do I just wire the 2.5mm into a 3A FCU and leave the 16A breaker? Is there any particular reason or benefit to having it on it's own circuit.
3. KITCHEN RADIAL TO RING
I currently have just 2 double sockets in the kitchen each 1 a radial from a 16A breaker. Because both cables run from the same point on the CU I would like to add more sockets inbetween ultimately turning this into a ring. I would like to add 1 more double, 1 single, an isolating switch for a 2400w single oven and 1 more single or an FCU for a cooker hood. I know the breaker will have to be changed to a 32A. Should I run the hood from a single socket with a plug or an FCU? Do I have to have another isolating switch for the cooker aswell as the hob or can they be wired into 1 dual switch and then independantly to the oven and hob using the 2.5mm and 4mm respectively?
4. CHASING IN KITCHEN
I'm going to have to chase cables in all sections of the wall mid, corners, up near the ceiling for cooker hood. Can I run these in conduit or do they have to be protected with metal? Can anyone provide a link to show me what I need to be looking for along the lines of metal mechanical protection if that is whats required as I can only seem to find armoured cable. Does the metal protection have to be earthed?
5. EXTEND LIGHT CABLE
Is it ok to extend a 1.5mm light switch cable using a junction box or should I run a fresh length. Would be much easier to extend. What AMP junction box should I be looking at for this cable. Is 16A ok?
Sorry if that's a lot to take in. Thought I'd get it all out in 1 go.
My house seems to have had a recent rewire and I have a new looking mem 2000AD CU.
1. HOB WIRING
I have a 6400w rated hob and there is already a cooker point wired with 4mm cable on a 32A breaker. I would like to reroute this cable without changing the length or extending it to run the hob and hob alone. Do I run the cable into an isolating switch 1st and then run some more 4mm to a hardwired cooker outlet? Is this all sufficient and in line with regs? User guide says 2.5mm and 25A so I presume this is ok for now but may not be adequate for an upgraded hob?
2. IMMERSION OUT BOILER IN
I have removed an old back boiler and am having a combi condensing boiler fitted. The old immersion (which has since taken a trip the scrap yard) was connected to a 16A breaker on 2.5mm cable. I would like to reroute this cable to run just the boiler. Do I just wire the 2.5mm into a 3A FCU and leave the 16A breaker? Is there any particular reason or benefit to having it on it's own circuit.
3. KITCHEN RADIAL TO RING
I currently have just 2 double sockets in the kitchen each 1 a radial from a 16A breaker. Because both cables run from the same point on the CU I would like to add more sockets inbetween ultimately turning this into a ring. I would like to add 1 more double, 1 single, an isolating switch for a 2400w single oven and 1 more single or an FCU for a cooker hood. I know the breaker will have to be changed to a 32A. Should I run the hood from a single socket with a plug or an FCU? Do I have to have another isolating switch for the cooker aswell as the hob or can they be wired into 1 dual switch and then independantly to the oven and hob using the 2.5mm and 4mm respectively?
4. CHASING IN KITCHEN
I'm going to have to chase cables in all sections of the wall mid, corners, up near the ceiling for cooker hood. Can I run these in conduit or do they have to be protected with metal? Can anyone provide a link to show me what I need to be looking for along the lines of metal mechanical protection if that is whats required as I can only seem to find armoured cable. Does the metal protection have to be earthed?
5. EXTEND LIGHT CABLE
Is it ok to extend a 1.5mm light switch cable using a junction box or should I run a fresh length. Would be much easier to extend. What AMP junction box should I be looking at for this cable. Is 16A ok?
Sorry if that's a lot to take in. Thought I'd get it all out in 1 go.