In one of my replies I stated that nothing could increase the tripping time.I find it a little hard to see how having loads connected to the circuit could increase measured RCD trip times.
No one has contradicted.
However, and I'm just theorising as I don't know exactly how the meter works.
What if, with the loads connected, there was a, say 10mA, leakage from L to E and the meter induces a leakage current from N to E, the first 10mA of which would counteract the existing fault.
Presumably this would increase the tripping time.
A ramp test would give a really high value too.
However if the existing leakage were from N to E this would reduce the tripping time but the fault may be discovered because the IΔn/2 test could also cause a trip (the existing fault may have to be slightly higher).
The ramp test value being correspondingly lower.