Hello,
I have had a problem occur in the bathroom whereby I was getting a strange tingle on broken skin while washing my hands in the bathroom. It felt faintly electrical so I switched the electricity of at the breaker and lo and behold it went away.
The only place where electricity could have possibly have come in contact with water in the bathroom is the towel radiator. Pipes run around the bottom of the wall while any cables run around the top so I can't see any way it could be anything else.
I disconnected the element and again that cured it. I noticed in the process of doing this that touching the earth conductors of the incoming feed and the element cable produced a bit of a spark, also touching the incoming earth resulted in a little shock (live was isolated) which I guess is suggestive of an earth fault somewhere.
So, after some disconnecting of cables and doing some basic insulation tests with a multimeter, I think I've isolated the problem to the cable between the fuse box and the switches for the bathroom (bathroom is on a radial circuit).
Resistance between live and earth conductors measures about 15kOhm. Cable is disconnected both ends so should effectively be open circuit. Other cables do read open circuit in a similar test.
Before I start ripping walls apart to try and replace this cable, I just wanted to reassure myself I'm not being an idiot and this does sound like it is the problem?
Thanks,
J
I have had a problem occur in the bathroom whereby I was getting a strange tingle on broken skin while washing my hands in the bathroom. It felt faintly electrical so I switched the electricity of at the breaker and lo and behold it went away.
The only place where electricity could have possibly have come in contact with water in the bathroom is the towel radiator. Pipes run around the bottom of the wall while any cables run around the top so I can't see any way it could be anything else.
I disconnected the element and again that cured it. I noticed in the process of doing this that touching the earth conductors of the incoming feed and the element cable produced a bit of a spark, also touching the incoming earth resulted in a little shock (live was isolated) which I guess is suggestive of an earth fault somewhere.
So, after some disconnecting of cables and doing some basic insulation tests with a multimeter, I think I've isolated the problem to the cable between the fuse box and the switches for the bathroom (bathroom is on a radial circuit).
Resistance between live and earth conductors measures about 15kOhm. Cable is disconnected both ends so should effectively be open circuit. Other cables do read open circuit in a similar test.
Before I start ripping walls apart to try and replace this cable, I just wanted to reassure myself I'm not being an idiot and this does sound like it is the problem?
Thanks,
J