G
Gazzza
Just started some testing with the multimeter, at one of the switches/ceiling roses that displays the apparent voltage using the neon tester when the switch is on.
So, at the ceiling rose, with bulb in or out, and the switch on or off, the meter readings are :
N-E is always 0 V
P-E is 237 V
P-N is 237 V
Then, also at the rose, switched live to earth reads 237V when the switch is on, 0 when the switch is off.
Switched live to N reads 237 V when the switch is on and reads 0 when it’s off.
I say 237, if I repeat the tests 5-10 mins later it might be 238, it might be 237. I’ve picked up readings as high as 239 and low as 236.
However at any one moment of doing the tests, flicking the switch does not show any differences in the readings between P-E and P-N. And N-E is always 0 V.
(as P-E and P-N always gives me the same reading this suggests to me its fluctuations in the main supply ? Is that normal ? )
At the switch for that light, everything is as you might expect:
With the switch off:
P-E is 237 V
P-switched live is 237 V
Switched live–E is 0
With the switch flicked on the switched live becomes live, and therefore Switched Live to Earth reads 237 V.
In other words flicking the switch on has no effect on the meter reading. Live to Earth gives 237 V. Turn on. Live to Earth still gives 237V, as does the switched live to earth when on.
That to my (simple) mind seems correct. Does that look ok ? (or am I oversimplyfing)
In terms of resistance I wasn’t entirely sure what I was supposed to be measuring. With the MCB off for that circuit and the bulb out at that rose, N-E at the ceiling rose reads 1.4 ohms. P-N and P-E does give me any reading.
(the meter stays on 1 which is its default display in resistance mode).
G
So, at the ceiling rose, with bulb in or out, and the switch on or off, the meter readings are :
N-E is always 0 V
P-E is 237 V
P-N is 237 V
Then, also at the rose, switched live to earth reads 237V when the switch is on, 0 when the switch is off.
Switched live to N reads 237 V when the switch is on and reads 0 when it’s off.
I say 237, if I repeat the tests 5-10 mins later it might be 238, it might be 237. I’ve picked up readings as high as 239 and low as 236.
However at any one moment of doing the tests, flicking the switch does not show any differences in the readings between P-E and P-N. And N-E is always 0 V.
(as P-E and P-N always gives me the same reading this suggests to me its fluctuations in the main supply ? Is that normal ? )
At the switch for that light, everything is as you might expect:
With the switch off:
P-E is 237 V
P-switched live is 237 V
Switched live–E is 0
With the switch flicked on the switched live becomes live, and therefore Switched Live to Earth reads 237 V.
In other words flicking the switch on has no effect on the meter reading. Live to Earth gives 237 V. Turn on. Live to Earth still gives 237V, as does the switched live to earth when on.
That to my (simple) mind seems correct. Does that look ok ? (or am I oversimplyfing)
In terms of resistance I wasn’t entirely sure what I was supposed to be measuring. With the MCB off for that circuit and the bulb out at that rose, N-E at the ceiling rose reads 1.4 ohms. P-N and P-E does give me any reading.
(the meter stays on 1 which is its default display in resistance mode).
G