Just got back from inlaws & needed warming up - however the HW worked, but the CH did not. I have a potterton puma 100e boiler.

Pressure is fine, tried switching off/on at mains & checked clock - all ok. However CH will not turn on at all, even though HW is fine. Called someone but not sure when they will visit.

I noticed a few other threads on the lines of this, but no definitive solution.

Would be grateful for your advice :confused:
 
Sponsored Links
cheers - will give this a try tomorrow... when I have stopped shaking!
 
:idea: THe 2 most common causes of this fault are a dripping hot tap keeping the wax capsule open or the hot water microswitch is stuck in the on position. ;)
 
Sponsored Links
drboilerfix said:
:idea: THe 2 most common causes of this fault are a dripping hot tap keeping the wax capsule open or the hot water microswitch is stuck in the on position. ;)

err micro switch stuck on

think that might be noticable by the noise and the water flying out of the prv :LOL:
 