Before you try anything drastic try replacing ( or in practice just remove ) the DHW flow limiter.
This is a plastic bit with a rubber "O" ring within the cold water inlet bits at the back of the boiler. Tricky to get at but is probably the problem as the ring swells up and is best removed completely.
The part you have replaced limits DHW outlet flow until the boiler has heated up and rarely gives a problem.
Tony