Hi, recently my boiler (not sure if 40 or 50) has started to make banging and weezing noises after running for quite awhile. I have checked the pump and it is running fine with the mid range speed selected and all radiators hot. suspected the boiler thermostat (upper of the two on the boiler outlet pipe, i think?). I removed the thermistor and substituted it with the temp probe from multimeter. When the temp indicated 82 Deg C, the weezing started followed by slight banging, i switched off boiler at main switch and noticed the temp continue to rise to 97 Deg C. With the probe still in place, i positioned the thermistor so it was touching the outlet pipe and started boiler again. With the boiler thermostat at lowest setting, boiler shut down at 78 Deg C, no banging. With probe and thermistor in same position i moved thermostat away from min setting and started boiler again, this time temp rose to 84 Deg C followed by banging. So it seems that with the boiler thermostat at any position that min, the temp rosed quite high and the banging started. Is this a faulty thermistor or, sludge in bottom of Heat Exchanger. If the latter is it ok to use DS4 (seen mentioned on forum) for my open circuit system of 12 years old and how much do i use for a 12 rad system? I replaced the CB 2 1/2 years ago but now can't find anything to indicate whether it is a 40/50 or other!.
Many thanks
Many thanks