Potterton Suprima 70 L with Danfoss thermostat- new PCB & flow sensor - Fixed one issue now always on?

Joined
22 Aug 2022
Messages
5
Reaction score
0
Country
United Kingdom
So I moved into a house with a Potterton Suprima 70 L about 7 years ago, never really fiddled with the heating much as it just seemed to work on auto when required and be "off" in summer, hot water was always hot, great times. Those ended earlier this summer when the hot water ran out, boiler wouldn't fire after running the blower for about 7 seconds, turned immersion on and started troubleshooting.

Having never looked at a boiler before I was a bit out of my depth and spoke to a local plumber & gas engineer who had done work on a number of houses built at the same time with the same boilers, he popped round and did some bits, checked the air pressure sensor and it seemed ok (listened for the click I assume as didn't have a multimeter) and suggested swapping the PCB, I'd seen the new ones were nearly £300 do picked up a refurb for £70, this didn't solve it, no gas, no spark.

I kept on trying bits and after probing around with the multimeter for a while I discovered the mod to add the water flow sensor in series with the airflow sensor, this appeared to be the issue, discovered there's a pump behind the laundry rack the previous owners had installed which had seized, popped that off and disassembled and graunched as much iron grit out of it as I could and it now runs a treat, boiler instantly fired up which was exciting with half the covers off!

Fast forward a couple of hot summer days and I'm in the kitchen and realise the boiler is happily cracking on despite the hot water demand being off from the danfoss thermostat?! There's another danfoss box up in the hot water tank cupboard - is that likely to be it's power switch with fuse above the immersion switch? Anyway what do I need to do to fix the demand side? both Potterton PCB's seem to work fine, unless they've both failed in this exact same way? I'm more suspicious that after being turned off for a couple of weeks something has happened with the danfoss?
 
Sponsored Links
Sounds like a failed motorised valve. Either the head or complete valve would want replacing if this is the case.
 
Photos are always good.
e.g. Danfoss box? Could be all sorts of things.
 
Pictures below,
I'm not sure but I don't think it's a valve, more likely something reset in the danfoss manager bit because it was switched off for a couple of weeks

20220823_181330.jpg

20220823_183208.jpg
 
Sponsored Links
The motorised valves are the white blocks on the pipes right? Why would they effect the fact the boiler lights even when the little management unit has both hot water and central heating turned off? I know CBW said it but I don't understand how the two can possibly be related?
 
That fixed it, Thanks! The HW valve was jammed open, put a spanner on it and gently worked it back and forth till it was easy to move without the spanner, now all is working well,

I see how it works now, that seems really strange to me but I guess it's a kind of "pull" demand, if the thermostat says it's too cold, open the valve, once the valve is open then light the boiler to heat water?

Because it's the bit you interact with/what stops working I assumed the boiler would be the main control
 