You don't want the cat5 in the same duct as power so 4m duct length + up/down on both ends, ideally 20cm apart.
Beebopper";p="3235741 said:Still not sure what elec cable to use from the house, 2.5mm or 6mm?
Your electrician said "2.5mm armoured is more than enough,"
The second electrician did, but the first one said 6mm² - hence I presume, the OP's question.Your electrician said "2.5mm armoured is more than enough,"Still not sure what elec cable to use from the house, 2.5mm or 6mm?
The second electrician did, but the first one said 6mm² - hence I presume, the OP's question.Your electrician said "2.5mm armoured is more than enough,"Still not sure what elec cable to use from the house, 2.5mm or 6mm?
Kind Regards, John
It really all comes down to the load. You have said "a 1.5kw heater, lights (led) and computer equipment. Not much more, maybe a phone charger. 17m run". As the second electrician has said, for that load, 2.5mm² would be more than enough. However, the question arises as to what additional power requirements you might possibly have in the future. If you're "sure" that you will never need more, then fair enough. However, given the relatively small differential in cost between different sizes of SWA (and the great hassle of burying it!), I personally would be inclined to go for larger than 2.5mm² SWA for any sort of outhouse, to provide some degree of 'future proofing".That's right John, I've found a chart on this site that cross references cable size to load and to my (very limited) knowledge on this I see it as 2.5mm, but obviously not 100% as I should be trusting the trade, but have two opinions!The second electrician did, but the first one said 6mm² - hence I presume, the OP's question.
Use this one://www.diynot.com/pages/el/el004.php
Depends on the installation method, grouping factors, ambient temperature factors etc, and, of course, how long it is.That chart above says 2.5mm goes up to 4.8kw.
Indeed. However, the difference in price between 4mm² and 6mm² is so relatively small that I personally might well be tempted by the additional 'future-proofing' provided by the latter!Ok thanks for the honest advice John, much appreciated – I’m not 100% sure if any further power requirements may be needed in the future, I suppose it could be possible - I think the first sparky was using your train of thought, but second one looking at in reality what would be used. Maybe 4mm is a good compromise!
Fair enough.Again thanks for all your help guys, I have in fact sourced another sparky who has ben really helpful and gone through the load / numbers with me and recommends 4mm cable. He's coming to install and sign off in the next week or so.
If you're talking about flexible conduit with a corrugated interior, then pulling a significant length of any sort of cable through it can sometimes be 'fun', particularly around bends, because of the corrugations.My responsibility is to sort the cat5 from the house to the shed, and he recommends it goes in conduit rather than clipped like the armoured SWA will be. ... I know that ban-all-sheds said the flexi stuff isn't suitable before, was that just for electrics or for all cables? Do I need the twin wall again for the cat5?
The problem with 20mm flexible conduit is that the combination of its small size and non-smooth walls makes it very difficult to pull an armoured cable through. You were talking about 6mm² cable - the diameter of that is 17 - 17.5mm. There would be zero chance of pulling that through ribbed conduit which inside is 1mm wider, at best. Even smaller cables are likely to snag on bends.
Cat5 would not be such a problem, it's smaller and more flexible, but might still snag on bends. Why are you so keen to avoid using twin wall ducting?
It seems that the idea of running teh SWA in ducting has gone out of the window:The problem with 20mm flexible conduit is that the combination of its small size and non-smooth walls makes it very difficult to pull an armoured cable through.
The sparky will be laying the armoured cable direct on sand and marked up appropriately.
Indeed. Although it would be OK for very short runs, I personally wouldn't want to pull a significant length of even Cat5 through a duct with internal corrugations, particularly if there were significant bends involved.Cat5 would not be such a problem, it's smaller and more flexible, but might still snag on bends. Why are you so keen to avoid using twin wall ducting?
Oh - if it's that short, I would not be too worried.It will only be the cat5 / telephone going through conduit and the run is approx. 2m, so not a great length to get it through.