When your meter leads aren't connected to anything you get a reading of 0v so the switch live could be open circuit.
Therefore the SL conductor is not continuous.Multimeter says there's 240V across both the permanent live and neutral, and the switched live and neutral, at the three pole isolator. However the same test at the fan terminals gives 240V between permanent live and neutral, but zero V between switched live and neutral (with the lights on).
Not open circuit - just no voltage on SL terminal.Ok, so assuming it's an open circuit from switched live to neutral
No - it's a problem with the SL conductor.but 240V from perm live to neutral, it must be a problem in the switched live part of the fan, no?
Ok. If you have reported correctly that will be 0V.I'll try switched live vs earth tomorrow and see where that gets me!
There isn't much to draw.I'll also draw a diagram tomorrow of how I've wired it up, but in the mean time...
That would confirm that those two cables where continuous, so perm live and neutral are okay.Wire from isolator to fan must be continuous surely, or there wouldn't be a potential difference between the perm live and the neutral at the fan?
Which does not really tell us anything as you would expect it to be anyway.There was 0V between the perm live and the switched live at the fan
In theory you are testing the same phase against each other, so you would expect a zero reading if open or closed.which is weird because that would suggest both were at 240V.
No it wouldn't you first test between line and neutral confirms you have both of them in place.which if true would suggest a problem with the neutral
The neutral seems fine, it was not used when testing across the line and switch line, so that is irrelevant but was tested between line and neutral where results were satisfactory.yet if the neutral was the problem I wouldn't have 240V between perm live and neutral!
I meant was the light in operation at the time of testing, so that the switch live was actually energized (providing continuity is satisfactory).Prentice, do you mean the isolator switch? The isolator was closed when I was testing, as in it was on. When I tested I turned on the light switch and the isolator.
If you have not yet confirmed continuity of all conductors this would be hard to assume.This one has me stumped. Must be a broken fan!
And that you have proved beyond your confidence that it islots of lessons learned indeed. One of which was: don't assume you've made a mistake when you're confident the wiring you've done is correct!