Right, where do I begin!
Fitting a new kitchen before chrimbo and decided to take the plunge, stretch the finances to get the economy going again (!), and get a new boiler while I was at it (boiler lives in a nice new kitchen cupboard now).
The plumber stated our wiring was a bit funny and 'not normal' to the wife before he left but all seemed to work ok he said.
About a week after the new boiler was fitted we noticed the whole system was running constantly (boiler & Pump on all the time).
Phoned up some drayton stockists (we have a Y Plan system with an HTS3, and RTS1 an LP522 and an MA1 mid position valve) who agreed it was all wired wrong and sent me the correct wiring diagram for our installation. Armed with that I re-wired all in correctly.
Problem still remained.
Tested various things and replaced both stats (hts3 was defo's shot) and the programmer. All was working fine.
About a week later the same issue raised its head again. I have done all the tests (remove orange wire) to check it's not the MA1 and even bought a new head for it and wired it in - still no joy.
Anyone got any ideas?
I noticed last night (re-wiring it all for a second time!) that the MA1 responds to the central heating being turned on and off but there's no response to the hot water being turned off. neither of the thermostats seem to make any difference...
Does anyone have a list of voltages that should be at each terminal in certain conditions. The terminal with grey wire from the MA1 never drops below 80V but I have no idea if that's normal or not.
Fitting a new kitchen before chrimbo and decided to take the plunge, stretch the finances to get the economy going again (!), and get a new boiler while I was at it (boiler lives in a nice new kitchen cupboard now).
The plumber stated our wiring was a bit funny and 'not normal' to the wife before he left but all seemed to work ok he said.
About a week after the new boiler was fitted we noticed the whole system was running constantly (boiler & Pump on all the time).
Phoned up some drayton stockists (we have a Y Plan system with an HTS3, and RTS1 an LP522 and an MA1 mid position valve) who agreed it was all wired wrong and sent me the correct wiring diagram for our installation. Armed with that I re-wired all in correctly.
Problem still remained.
Tested various things and replaced both stats (hts3 was defo's shot) and the programmer. All was working fine.
About a week later the same issue raised its head again. I have done all the tests (remove orange wire) to check it's not the MA1 and even bought a new head for it and wired it in - still no joy.
Anyone got any ideas?
I noticed last night (re-wiring it all for a second time!) that the MA1 responds to the central heating being turned on and off but there's no response to the hot water being turned off. neither of the thermostats seem to make any difference...
Does anyone have a list of voltages that should be at each terminal in certain conditions. The terminal with grey wire from the MA1 never drops below 80V but I have no idea if that's normal or not.