Pump runs continuously (no CH/HW call; boiler switched off)

Sponsored Links
Hi again,

Q1: Is the thermistor mentioned below (Potterton Performa 28i - system was "humming" at 4am) the same thing as the "thermostatic sensor" of my Baxi Solo 3 PF?

Q2: And is it also the same thing as its "integral frost-stat"?

gazthepottertonengineer said:
its normal for it to take upto 5 mins as this is the anti cycle on the boiler working but if its much more than that then its more than likely to be pcb ;) try replacing the temperature thermistor first though just to rule it out as its cheap and very easy to replace as its in a dry pocket :LOL:

This is exactly what the problem was. This switching problem only occured when the boiler was in pre-heat mode. Two thermisors were replaced, which required a small amount of draining-off water from the boiler as one of the thermisors was on a pipe containing water.
 