ok. i have an old servowarm elite 50 and the the pump seems to cut out occasionally causing the water to kettle and then this cuts off the gas through the high temp cut out.. (i'm guessing here from advice i have been given elsewhere).
Anyway i called an engineer out who said the system is sludged up and this is prob stopping the pump.. this also causes excessive gassing which trips out the over heat.
His advice was to change the pump, add another AAV and desludge the system and add anti knock.,
Now i can find my way around a pump and some pipework so i drained the system down.. cleaned the pump head and ran antisludge for a week.. (pump still cut out)..
flushed it all through and then drained it down till clear.. (after refilling running and emptpying a few times)
then added anti knock and inhibitor.
next day all fine.
next day back to same problem
there is already an aav which works cos it always kicks out air when the pump cuts out.
do i really need another one?
is it likel;y that the pump is acutally shot.. it runs fine when it does run.. but i'm wondering if there is a problem with the boiler cicuit board.
the timer is fine.. cos i'ce just replaced that too anyway (it was an old simple one and i addeed a 5/2 one with 3 day settings rather than 2)
Any advice would be appreciated..
Anyway i called an engineer out who said the system is sludged up and this is prob stopping the pump.. this also causes excessive gassing which trips out the over heat.
His advice was to change the pump, add another AAV and desludge the system and add anti knock.,
Now i can find my way around a pump and some pipework so i drained the system down.. cleaned the pump head and ran antisludge for a week.. (pump still cut out)..
flushed it all through and then drained it down till clear.. (after refilling running and emptpying a few times)
then added anti knock and inhibitor.
next day all fine.
next day back to same problem
there is already an aav which works cos it always kicks out air when the pump cuts out.
do i really need another one?
is it likel;y that the pump is acutally shot.. it runs fine when it does run.. but i'm wondering if there is a problem with the boiler cicuit board.
the timer is fine.. cos i'ce just replaced that too anyway (it was an old simple one and i addeed a 5/2 one with 3 day settings rather than 2)
Any advice would be appreciated..