Hi
We have a workshop which is being supplied from the house via a 40A Type B MCB. In the workshop we have a dedicated consumer unit.
In the workshop we have 2 x 3kw fan heaters to be controlled via a room stat / contactor ( relay ).
We also have a 3kW vented water heater and a 3hp ( 2.2kw ) air compressor.
It is not possible to change the cable running from the house.
In the winter I expect that both fan heaters will be running, albeit via the room stat ( the workshop is well insulated ), the water heater will be on, albeit controlled via the thermostat on the unit.
Now when the air compressor kicks in to charge the cylinder I calculate that the total loading being drawn at that time will be :
( 3kW x 2 ) plus 3W plus 2.2kw = 11.2kw albeit only while the air compressor is running.
Based on 230Vac I calculate the theortical current drawn will be 48.7A.
Will the 40A MCB take the loading for a period based on the MCB time current characteristics or will it trip immediately ?
Cheers
We have a workshop which is being supplied from the house via a 40A Type B MCB. In the workshop we have a dedicated consumer unit.
In the workshop we have 2 x 3kw fan heaters to be controlled via a room stat / contactor ( relay ).
We also have a 3kW vented water heater and a 3hp ( 2.2kw ) air compressor.
It is not possible to change the cable running from the house.
In the winter I expect that both fan heaters will be running, albeit via the room stat ( the workshop is well insulated ), the water heater will be on, albeit controlled via the thermostat on the unit.
Now when the air compressor kicks in to charge the cylinder I calculate that the total loading being drawn at that time will be :
( 3kW x 2 ) plus 3W plus 2.2kw = 11.2kw albeit only while the air compressor is running.
Based on 230Vac I calculate the theortical current drawn will be 48.7A.
Will the 40A MCB take the loading for a period based on the MCB time current characteristics or will it trip immediately ?
Cheers