radiator balancing with multiple zones

[The minimum flow rate quoted by manufacturers is normally calculated for the peak output with the stated temperature differential. So Vaillant quote 20.3 litres per minute for the 428 with a 20C differential. (My calcs give 20 litres per minute.)
That's a minimum flow rate at full power for getting the heat out of the boiler!
Agreed. But with an on/off boiler its either running at full whack, which needs the stated flow, or not at all.

Agile said:
Its not the same as the minimum flow rate to enable the boiler to control its heat output.
I don't understand what you mean :confused: Are you talking about a modulating boiler?
 
Sponsored Links
Agreed. But with an on/off boiler its either running at full whack, which needs the stated flow, or not at all.

I don't understand what you mean ? Are you talking about a modulating boiler?

All modern domestic boilers modulate, condensing or not!

Tony
 