When balancing, close all the lockshields, and open by half a turn. No more.
Then run the CH for half an hour.
Use the temperature sensors in the skin of your hand. The flow pipe should be "too hot to hold" and the return pipe should be "too hot to hold for long."
For any that are not, open or close the lockshielc by no more than a quarter turn, and continue running the CH for another half hour before checking again. Do not alter any by more than a quarter turn in half an hour. The adjustment is very slight, and it is all at the "nearly closed" position.
Once flow seems correct, and has been for half an hour, feel them all over. Top, bottom, sides, middle. There should be no cold patches. They should be hotter at the top than the bottom. If any are excessively hot, you can tighten the lockshield by a quarter turn.
Some rooms may have rads that are too big, and you can reduce their output by tightening the lockshield. A radiator that is too small for the room cannot be made more powerful.
Write the adjustments in a notebook and tie it to the boiler.