Me again - just been to B&Q they do a replacement Sunvic three port valve for £40 - is this something a novice could do or do I need a plumber - I assume I need to drain the system down ?
You may not need to change the complete valve - just the actuator (box on top).
1. Have you checked that the valve is the correct way round? The port marked A should go to the radiators; the port marked B to the HW cylinder. If it's the wrong way round, that needs to be put right first. You should also check the valve has been wire correctly.
White to room thermostat output
Grey to programmer HW OFF and HW cylinder stat Satisfied.
Orange to HW cylinder stat Call and boiler on
Blue to neutral
Earth to earth!
2. Have you checked if the valve spindle is stiff? Remove the actuator and try rotating the valve spindle - it may only move 20° or so from port A open to port B open - depends on the valve. A stiff valve can sometimes be eased with a small amount of WD40 or similar lubricant.
If the valve is OK and wiring OK but the problem is still there, replace the actuator.