this is called "exercising" and could loosen things up that have been sitting there doing nothing for 5 years.
Rubbish, You would be adding to the wear and tear of the mechanism and thus shortening it's life span.
this is called "exercising" and could loosen things up that have been sitting there doing nothing for 5 years.
The standard tests prove that. The actual tripping current is irrelevant. All it needs to do to satisfy the requirements is not trip at half the rated residual operating current; operate within 300mS for BS EN types (200mS for older BS types) at I delta n, and within 40mS at 5 I delta n.Well, it's going to prove the RCD is satisfactory
I don't agree that it's appropriate. The RCD should be regarded as failed if it doesn't trip in the required time. Exercising it to create a false pass is certainly not the correct course of action.That is sometimes appropriate, but it addresses a problem which is the opposite of what the OP is experiencing.
I don't understand what you mean.The standard tests prove that.Well, it's going to prove the RCD is satisfactory
I would have thought that was the only relevant thing in such a case as this.The actual tripping current is irrelevant.
Yes, we all know that but only one of those is relevant to the problem in this case.All it needs to do to satisfy the requirements is not trip at half the rated residual operating current; operate within 300mS for BS EN types (200mS for older BS types) at I delta n, and within 40mS at 5 I delta n.
16mA is acceptable for a 30mA RCD. So it is within tolerance.If it trips at 16mA then it is more likely to trip more often, or if it does trip at ½IΔn, maybe it trips at 5mA, then it is unsatisfactory.
I would imagine there is some threshold for 'transient' dips/spikes on the network, especially when dealing with the aftermath of a storm. Either way, I don't have the time or inclination to get into a correspondence battle with the DNOInteresting- and worth an email probably to your electricity supplier in the first instance since the low number is outside tolerance for UK electrical supply. They'll probably swerve and point you at the DNO for your area but could be an amusing hobby if you wanted one. Does the UPS app give you a pretty graph- if so then screenshot it & attach it to the email
Ah yes, valid point (Storm Thing has been a bit of a non-event here, an excess of surface water but otherwise nowt to write home about)I would imagine there is some threshold for 'transient' dips/spikes on the network, especailly when dealing with the aftermath of a storm. Either way, I don't have the time or inclination to get into a correspondence battle with the DNO