I have a Ravenheat RSF84ET boiler which I installed about 3 years ago and whilst the CH side is fine, the DHW does not control as well as I would like. Incoming water temperature is about 15C at the moment and if I open a tap to a flow rate of 8 L/min then with the thermostat set to max the hot water temp settles at 51C and with the thermostat set half way the temp is 47C. So far so good. However if I set the thermostat to min then the gas valve does not modulate sufficiently to achieve a stable temperature before the gas is cut off. After a few seconds the burner relights and the controller tries again to stabilize and again fails. This results in a fluctuating water temp of 32C - 43C. If the flow rate is reduced to 4 L/min then no stable temp is possible and the temp ranges are 47C-59C, 41C-53C and 33C-43C respectively for the 3 thermostat setting.
If I check the voltage across the modulator coil I find that it starts at 15.5V at first and then gradually reduces to 7.3V and it sits there unable to go any lower. This corresponds to a burner pressure of about 4 mbar and this is not low enough to avoid overtemp. (Note that the pressure does not begin to fall below 8 mbar until the voltage is below 12V)
Additional investigation shows that the modulator can adjust the burner pressure from max pressure (8 mbar) down to min pressure (1.5 mbar) if the input voltage range is about 4 to 12 volts and if this was the case then I am sure that a stable water temp. would be possible over a range of water flow rates and a range of thermostat settings.
Does anyone know what the design spec. is for the modulator voltage output on the controller board ?
I suspect the controller but it's an expensive part to replace if it is not the source of the problem.
My next move might be to draw the circuit diagram of the controller circuit board and see if I can identify any faulty component which might be producing an output voltage which is too high.
Sorry about the long post but I felt that someone out there might find these observations useful.
If I check the voltage across the modulator coil I find that it starts at 15.5V at first and then gradually reduces to 7.3V and it sits there unable to go any lower. This corresponds to a burner pressure of about 4 mbar and this is not low enough to avoid overtemp. (Note that the pressure does not begin to fall below 8 mbar until the voltage is below 12V)
Additional investigation shows that the modulator can adjust the burner pressure from max pressure (8 mbar) down to min pressure (1.5 mbar) if the input voltage range is about 4 to 12 volts and if this was the case then I am sure that a stable water temp. would be possible over a range of water flow rates and a range of thermostat settings.
Does anyone know what the design spec. is for the modulator voltage output on the controller board ?
I suspect the controller but it's an expensive part to replace if it is not the source of the problem.
My next move might be to draw the circuit diagram of the controller circuit board and see if I can identify any faulty component which might be producing an output voltage which is too high.
Sorry about the long post but I felt that someone out there might find these observations useful.