Agreed. In fact, I think it's the only honest approach (unless some people hve managed to discover a lot more information than I have).I agree with that, I can't find enough information either, and like you I would note it in report, but likely would not give it a code.
As things are, I really don't think that (in relation to a standard domestic installation) I could honesty say that I yet know enough to be able to even "recommend" that a Type AC RCD be replaced (C3), let alone that I knew enough to declare that it was sufficiently "potentially dangerous" to require "urgent remedial action" (C2).
True, with our degree of relative ignorance, we could not say that it was necessarily "wrong", but I think it would be appropriate (and justified) for us to ask for an evidence-based justification for the coding.However if I find some one else has given it a code, I could not say that's wrong either.
As far as I am concerned, the type of RCD we have been using extensively (almost universally, I think) in the UK for 30-40 years (or whatever) "remains innocent until proven guilty" - so, from my viewpoint, it is down to the person who 'codes' a Type AC RCD to justify what they have done. Their argument obviously has to be good enough to over-ride ...
BS7671:2018 said:531.3.3 Types of RCD
Different types of RCD exist, depending on their behaviour in the presence of DC components and frequencies. The appropriate RCD shall be selected from the following: ......
For general purposes, Type AC RCDs may be used.
Kind Regards, John