I have been asked to convert a mess room supply which is curently a TN-C-S to a TT.
Before I disconnected the supply and converted it i had the followng readings.
Ze = 0.21 ohms
PFC = 1.01kA
x1 = 28.1 (30mA)
x5 = 8.9 (30mA)
I am no longer using the earth supplied via the swa and have fitted a new earth rod and have taken following readings
Ra = 69.2 ohms
PFC = 2kA
The problem I'm having now is the 30mA rcd will not trip on any test?
The RCD worked fine before i converted it over to the new earthing system. Any ideas why it does not work now?
Cheers.
Rob