Thanks to all for your advice. If you're interested, here is what I did in longwinded format; if not, the summary is that it is mostly fixed with one remaining doubt.
After reading a few faqs about wiring and CU's I felt confident enough to have a go. I turned off the double red switch and started by simply checking the RCD neutral bar against the earth bar and found its resistance was essentially zero. Repeated this for the non-RCD neutral which was also zero.
Then I realised that in order to bypass the RCD they had connected both neutral bars together and both buzz bars together. I removed these interconnects, put the safety cover back on and switched the power back on.
I set all MCB's on and then tried to set the RCD, but it immediately tripped (no surprises there). I then turned all the RCD MCB's off and tried them one at a time with the RCD on and found that only one of them caused it to trip. However, I didn't know which circuit it was. It had two wires going into it and either of them caused the trip and so I thought it was probably a ring main as it was on the RCD side and was not the really thick cable (which I guess goes to the cooker). With this MCB pulled still I checked the sockets downstairs and they had no power so I assumed this is where the problem lay.
I therefore turned the main switch off again and rechecked. The neutral/earth resistance: for the RCD side was still zero, for the non-RCD side it was 400 Ohms.
I removed each neutral wire in turn and checked it against the earth. On the RCD side I found 1 large wire (ie. mulitple strands) had a zero resistance and all the others were infinite(well off the scale). On the non-RCD side I found 1 wire with 400 Ohms and all the others were infinite.
I then started to check all the downstairs sockets resistance from the earth pin to the neutral.
At first I thought there were no problems - I was testing resistance from earth pin to neutral with my meter set to beep mode and it was dark. However, I then noticed some of the sockets were giving around 350 ohms resistance which was not enough to cause my meter to beep, but obviously is not right.
I went back to the CU and removed both the suspect RCD side neutral wire(0 ohms) and the non RCD side neutral wire(400 ohms) and went back to test the sockets. The 400 ohm sockets were now OK. Eventually I found several others with zero resistance.
On opening them I found 2 of them had unshielded earth cables that were actually touching the neutral cable exposed copper part. I put plastic earth sleeves on them and trimmed and reconnected the neutrals so that no bare copper was extending from the terminal.
Having done this and put the lot back together I was dismayed to find a N-E short again on one of them. Close inspection revealed a nick in the neutral cable that only chafed on the metal box when the socket was screwed in.
I replaced the damaged wire and put everything back together and it all now works - the RCD sets and the Test button makes it pop.
The only thing I am left wondering about is the 400 Ohm N-E fault on the non RCD side which I thought would be a lighting circuit. However, having written all this I now realise it must be connected to one of the downstairs rings where I saw the 350 ohm faults before. Then again, maybe I tested those sockets whilst the neutral bars were connected together with the zero ohm RCD neutral disconnected, in which case I guess all neutrals would have shown an earth fault.
More to investigate tomorrow.
However, it seems that what the guys who did the job an Saturday said was fair and true. Will probably get them to look at the remaining N-E fault and also to fix a few DIY shockers from the previous owner (outside socket wired up via a single pole light switch to an indoor socket, metal light switch inside that has no earth connection)
After reading a few faqs about wiring and CU's I felt confident enough to have a go. I turned off the double red switch and started by simply checking the RCD neutral bar against the earth bar and found its resistance was essentially zero. Repeated this for the non-RCD neutral which was also zero.
Then I realised that in order to bypass the RCD they had connected both neutral bars together and both buzz bars together. I removed these interconnects, put the safety cover back on and switched the power back on.
I set all MCB's on and then tried to set the RCD, but it immediately tripped (no surprises there). I then turned all the RCD MCB's off and tried them one at a time with the RCD on and found that only one of them caused it to trip. However, I didn't know which circuit it was. It had two wires going into it and either of them caused the trip and so I thought it was probably a ring main as it was on the RCD side and was not the really thick cable (which I guess goes to the cooker). With this MCB pulled still I checked the sockets downstairs and they had no power so I assumed this is where the problem lay.
I therefore turned the main switch off again and rechecked. The neutral/earth resistance: for the RCD side was still zero, for the non-RCD side it was 400 Ohms.
I removed each neutral wire in turn and checked it against the earth. On the RCD side I found 1 large wire (ie. mulitple strands) had a zero resistance and all the others were infinite(well off the scale). On the non-RCD side I found 1 wire with 400 Ohms and all the others were infinite.
I then started to check all the downstairs sockets resistance from the earth pin to the neutral.
At first I thought there were no problems - I was testing resistance from earth pin to neutral with my meter set to beep mode and it was dark. However, I then noticed some of the sockets were giving around 350 ohms resistance which was not enough to cause my meter to beep, but obviously is not right.
I went back to the CU and removed both the suspect RCD side neutral wire(0 ohms) and the non RCD side neutral wire(400 ohms) and went back to test the sockets. The 400 ohm sockets were now OK. Eventually I found several others with zero resistance.
On opening them I found 2 of them had unshielded earth cables that were actually touching the neutral cable exposed copper part. I put plastic earth sleeves on them and trimmed and reconnected the neutrals so that no bare copper was extending from the terminal.
Having done this and put the lot back together I was dismayed to find a N-E short again on one of them. Close inspection revealed a nick in the neutral cable that only chafed on the metal box when the socket was screwed in.
I replaced the damaged wire and put everything back together and it all now works - the RCD sets and the Test button makes it pop.
The only thing I am left wondering about is the 400 Ohm N-E fault on the non RCD side which I thought would be a lighting circuit. However, having written all this I now realise it must be connected to one of the downstairs rings where I saw the 350 ohm faults before. Then again, maybe I tested those sockets whilst the neutral bars were connected together with the zero ohm RCD neutral disconnected, in which case I guess all neutrals would have shown an earth fault.
More to investigate tomorrow.
However, it seems that what the guys who did the job an Saturday said was fair and true. Will probably get them to look at the remaining N-E fault and also to fix a few DIY shockers from the previous owner (outside socket wired up via a single pole light switch to an indoor socket, metal light switch inside that has no earth connection)