had a RCD trip today.
When my wife Switched OFF the en-suite Main light.
More detail later on what I have tested and tried.
MCB's are Not tripping
Isolated the fault down to the bathroom/ensuite Lighting circuit. I removed the Live and Neutral at the consumer Unit. With this circuit disconnected every thing else on that RCD group is now working
Recent new installation.
New Consumer Unit fitted around Oct 2018
All Light units (Bathroom specific spec IP rating) NEW and ALL NEW Wiring in April 2019
By Electrician and Signed off , along with a lot of other work.
ONE question is
RCD tripping but not MCB indicates a neutral to Earth fault - is that correct
testing cable etc - I do not have a mega testing, only a Multimeter, so may not be able to isolate with testing
The faulty circuit provides
All Lights Bathroom / IP rated for zones etc
Centre Light in Bathroom , I have disconnected - still trips
Centre Light in Ensuite , I have disconnected - still trips
Wall /mirror Light in Ensuite, I have disconnected - still trips
Checked loft JB for water , damp etc - all fine
I have NOT yet checked
Shaver Socket
Bathroom LED lights
Any of the Switches - 3 Pull cords - 2 in ceiling and 1 2A architrave for LEDS
ALL the lighting cables runs via 1 off 20A JB in loft , about 6 T&E cables - going in
I took the top of JB off and moved all the cable around, - (I had an issue before with this Electrician and a JB poor quality Job, insulation split and shorted out, also A Double Socket Screw trapping Live and intermittent shorting live, MCB tripping - Now have a new electrician for rest of house rewire/work)
SO before I disconnect ALL these cable and test one by one with the RCD - I will try a multimeter, in case its a short, which the multimeter can detect.
BUT as i say i do not have a MEGA tester , NOT sure if i can get a cheap one
Any suggestions before i spending most of the day tomorrow in the loft removing all the cables from JB and then testing each circuit individually by checking the RCD trip and then hopefully fixing whatever is faulty.
Nothing happened / changed today , raining , but loft is dry in that area
the fault occured when the Ensuite Main light was switched OFF via the plastic ceiling pull cord
I have not checked the plastic ceiling mounted Pull cord switch , but i have completely removed the centre light, as mentioned.
Not sure if a switch can case this issue , as MCB is OK, JUST RCB , which i thought indicated a Neutral to Earth fault.
Thanks
When my wife Switched OFF the en-suite Main light.
More detail later on what I have tested and tried.
MCB's are Not tripping
Isolated the fault down to the bathroom/ensuite Lighting circuit. I removed the Live and Neutral at the consumer Unit. With this circuit disconnected every thing else on that RCD group is now working
Recent new installation.
New Consumer Unit fitted around Oct 2018
All Light units (Bathroom specific spec IP rating) NEW and ALL NEW Wiring in April 2019
By Electrician and Signed off , along with a lot of other work.
ONE question is
RCD tripping but not MCB indicates a neutral to Earth fault - is that correct
testing cable etc - I do not have a mega testing, only a Multimeter, so may not be able to isolate with testing
The faulty circuit provides
All Lights Bathroom / IP rated for zones etc
Centre Light in Bathroom , I have disconnected - still trips
Centre Light in Ensuite , I have disconnected - still trips
Wall /mirror Light in Ensuite, I have disconnected - still trips
Checked loft JB for water , damp etc - all fine
I have NOT yet checked
Shaver Socket
Bathroom LED lights
Any of the Switches - 3 Pull cords - 2 in ceiling and 1 2A architrave for LEDS
ALL the lighting cables runs via 1 off 20A JB in loft , about 6 T&E cables - going in
I took the top of JB off and moved all the cable around, - (I had an issue before with this Electrician and a JB poor quality Job, insulation split and shorted out, also A Double Socket Screw trapping Live and intermittent shorting live, MCB tripping - Now have a new electrician for rest of house rewire/work)
SO before I disconnect ALL these cable and test one by one with the RCD - I will try a multimeter, in case its a short, which the multimeter can detect.
BUT as i say i do not have a MEGA tester , NOT sure if i can get a cheap one
Any suggestions before i spending most of the day tomorrow in the loft removing all the cables from JB and then testing each circuit individually by checking the RCD trip and then hopefully fixing whatever is faulty.
Nothing happened / changed today , raining , but loft is dry in that area
the fault occured when the Ensuite Main light was switched OFF via the plastic ceiling pull cord
I have not checked the plastic ceiling mounted Pull cord switch , but i have completely removed the centre light, as mentioned.
Not sure if a switch can case this issue , as MCB is OK, JUST RCB , which i thought indicated a Neutral to Earth fault.
Thanks