That's odd - from that recent extract I'd say that the IEE Regs do mandate it, but the BRs don't.Spark123 said:Yeah, an electric shower is an electric water heater and not other equipment, the IEE regs as they stand don't mandate them being RCD protected.
Well you might say nah, but the following isn't a description of anything optional:Spark123 said:Nah, IEE regs don't mandate RCD protection for an electric water heater in zone 1 of a bathroom, normal regs apply i.e. must be suitable for the zone, supp bonding etc.
Is it?equitum said:In section 601-09-02 of the 16th edition said:The following fixed current using equipment may be installed in zone 1 if it is suitable for that zone:
(i) A water heater
(ii) A shower pump
(iii) Other fixed current using equipment which can reasonably only be located in zone 1 provided that
A) It is suitable for the conditions oof that zone
B) The supply circuit is additionally protected by an rcd with rated residual current not exceeding 30ma in accordance with regulation 412-06.
(iv) SELV current using equipment