I may have misunderstood you. You write a lot about 'nuisance trips' ('trips for no good reason') of RCDs/RCBOs being a common problem, and you appeared to be saying that such was your current experience. However, it now sounds as if you are saying that, in your current home, and like me, you experience virtually no such 'nuisance trips', and also that the same was the case in your mother's house. Is that correct?
Kind Regards, John
Yes it was just the house in Bryn-y-baal, Mold, however mother had 7 RCD/RCBO's and I have now in Llanfair Caereinion 14 RCBO's only the Byrn-y-baal house was limited to just two RCD's.
We are told we should work in times three when selecting RCD's, so for a 30 mA RCD no more than 9 mA drain to earth without fault, and a 30 mA would be protected by 100 mA and 100 mA protected by 300 mA and 300 mA protected by 1 amp etc. Not that this happens in the home, with domestic 30 mA supply is still protected by a further 30 mA with caravans and boats. However they do have battery backed lighting.
However we should check the leakage does not exceed 9 mA under normal running conditions, but lowest my clamp-on will measure is 100 mA all I can do is check the insulation resistance which uses DC so not really much good, and test with RCD tester that it does not trip at ½ rated current, which means could have 14 mA leaking and be unaware. Unlikely the RCD is bang on 30 mA but even 4 mA leeway is sailing a little close to the wind.
We are allowed equipment with up to 3.5 mA leakage, mainly due to EMC filters, and since through capacitors it will not be picked up with a DC insulation tester, and this leakage is only there when the appliance is plugged in. And we have traditionally tested the RCD with everything unplugged, in fact I watched a video talking about type AC and type A RCD's where the experts were talking about dropping tails to test, which to me seems crazy and in earth days main reason for RCD failure I found was due to strain on the casing from the cables in the terminals, more than once dressing cables was all that was needed to get RCD to pass.
There is also the question about DC desensitising the RCD, if it makes it more sensitive as claimed with high frequency noise that means it fails safe, but if we have something which injects DC for example a three port motorised valve in a Y plan central heating system, we really want to test with it all running to be sure not desensitised.
So we look at
BS7671:2008 said:
314.1 Every installation shall be divided into circuits, as necessary, to:
(i) avoid hazards and minimize inconvenience in the event of a fault
(ii) facilitate safe inspection, testing and maintenance (see also Section 537)
(iii) take account of danger that may arise from the failure of a single circuit such as a lighting circuit
(iv) reduce the possibility of unwanted tripping of RCDs due to excessive protective conductor currents produced by equipment in normal operation
(v) mitigate the effects of electromagnetic interferences (EMI)
(vi) prevent the indirect energizing of a circuit intended to be isolated.
which seems to say the RCD is considered as forming a circuit, OK BS7671:2018 may say something slightly different, but the point is if there is a possibility of unwanted tripping of RCDs then it should be split into more circuits. Before the person responsible for design selects a CU with just 2 RCD's he needs to be satisfied it is unlikely to cause unwanted tripping of RCDs, and if you can't measure the leakage current so are sure under 9 mA then best option is all RCBO's.
But when I did my inspection and testing exam, I was not told to check leakage, and I was told to test with all appliances disconnected. To some extent this makes sense, switching off PC's while in use can cause problems, and the switch mode power supply used in older PC's did cause problems, so it is the equipment we would normally switch off before testing which is the equipment most likely to cause problems.
So with mothers house moving the kitchen off the general RCD's and having a bank of 5 RCBO's was likely enough to ensure leakage was within limits, if we look at kitchen equipment, the induction hob, inverter washing machine, inverter fridge/freezer, and inverter freezer are all items likely to both freeze and cause RCD's to trip, and the oven with mineral insulated elements is also likely to cause a RCD to trip. So late mothers house could have 100 mA leakage and not trip as spread across 7 RCD devices, this house 200 mA as 14 RCD devices. OK unlikely to have maximum of 15 mA which should not trip a 30 mA trip on all circuits, but in the days of using type S 100 mA RCD's I do not remember problems with tripping, only when we went to 30 mA did we start having problems.
Never worked out why they are called high integrity consumer units, but having some key circuits on RCBO's seems to be enough to tip the balance and stop 'nuisance trips' as to if lights or sockets, or cooker is put on RCBO it seems this is often enough.
But since I could not measure the leakage, best idea seemed to be all RCBO. The other point is sockets split side to side, and lights split up/down, so could not arrange so when a RCD is tripped due to a fault not also plunged into darkness in some rooms. OK general power cut can plunge us into darkness, but that is not at same time as getting an electric shock, so sockets and lights should not be on the same RCD in any room, so in my house at least 3 RCD's are required.