Any ideas on this one folks, ring circuit, couple of sockets on the top floor are spurred, (two individual spurs from from two seperate parts of the ring), insulation resistance of >500 between all conductors, RCD tests at 36ms@ x1, 13.6@x5, all normal so far, no tripping at half current, 27ma on ramp test, can plug stuff in downstairs with no problem, but on the top floor the RCD trips, I tried again with nothing else plugged in to avoid a build up of fault current through several appliances, no difference, disconnected all the other circuits, no difference, swapped circuit onto other RCD, (just through curiosity and just in case of a borrowed neutral somewhere), did the same,
am I being thick here?
Also trips when taking zs readings, but only on top floor!!
tried loosening socket fronts in case of trapped neutrals etc,
am I being thick here?
Also trips when taking zs readings, but only on top floor!!
tried loosening socket fronts in case of trapped neutrals etc,