We (A company I sub to) installed the dis board in building 4 about 5 years ago, along with the pillar and ducts with split con to the other 3 outbuildings, until then they were fed with T&E suspended on catenary wires.
Not all of the work was done at the same time.
At the time I commented there were too many RCD's and suggested either RCBO at building 4 or RCD's in 1 to 3 but not both.
Since then there has been a small history of 'false tripping' but no significant.
All summer there has been a significant increase in tripping, including the main 500mA, and multiple visits had found no faults. The earlier visits had not resulted in a proper log but recently:
1) Building 2. - RCD tripped twice, RCBO tripped 3 times but not both - tripping times measure virtually the same on opposite ½ cycles so no surprise
2) Building 1. - 3 times RCD & RCBO & Main tripped.
3) both 1) and 2) of the above combined.
I've been on the last 2 visits and found scenario 1) and 3) on my second visit I added a 3ph RCD to building 1, running P & N through twice to make it more sensitive.
So far, amongst other things, I've checked all RCD's & RCBO tripping times. Ironically the only one which has failed and been replaced with a 2pole isolator is the toilet building 3.
Insulation across the whole system from the C63 MCB shows as ∞ with the 2 PIR's (buildings 3 and 4) disconnected and 5ft fluo unplugged (fluo measured as ∞ to earth).
All of the 'Z' readings are excellent.
Hardly a DIY problem but maybe another idea could help.
EDIT: While writing this I received an email saying the 'new' RCD for building 1 has tripped and reset OK.
Not all of the work was done at the same time.
At the time I commented there were too many RCD's and suggested either RCBO at building 4 or RCD's in 1 to 3 but not both.
Since then there has been a small history of 'false tripping' but no significant.
All summer there has been a significant increase in tripping, including the main 500mA, and multiple visits had found no faults. The earlier visits had not resulted in a proper log but recently:
1) Building 2. - RCD tripped twice, RCBO tripped 3 times but not both - tripping times measure virtually the same on opposite ½ cycles so no surprise
2) Building 1. - 3 times RCD & RCBO & Main tripped.
3) both 1) and 2) of the above combined.
I've been on the last 2 visits and found scenario 1) and 3) on my second visit I added a 3ph RCD to building 1, running P & N through twice to make it more sensitive.
So far, amongst other things, I've checked all RCD's & RCBO tripping times. Ironically the only one which has failed and been replaced with a 2pole isolator is the toilet building 3.
Insulation across the whole system from the C63 MCB shows as ∞ with the 2 PIR's (buildings 3 and 4) disconnected and 5ft fluo unplugged (fluo measured as ∞ to earth).
All of the 'Z' readings are excellent.
Hardly a DIY problem but maybe another idea could help.
EDIT: While writing this I received an email saying the 'new' RCD for building 1 has tripped and reset OK.