Not sure id be happy with that solar circuit feeding back into a RCD bank like that.
Hi Jono - what problems do you see with the above?
Not sure id be happy with that solar circuit feeding back into a RCD bank like that.
Hi Billy,
The issue I see with this is your RCD will cut the power in the event of a fault in a maximum of 0.4 seconds. However a Inverter can take upto 5 seconds to shut down following power loss. This means for upto 5 seconds your Inverter could be back feeding the circuits connected to the RCD bank.
Strikes me you need to get a competent and experienced electrician to sort this out. That price is far more than a 300 mA RCD would cost to a commercial operation.Billy Wolf said:They then found out that the 300ma RCD would cost about £380, so have ditched that idea due to cost
There would be no reason for the invertor to shut down as long as it has power coming from the solar array. It would continue to run feeding power to the house even though the safety devices in the CU had detected a fault that required power to be removed. That is extremely dangerous.However a Inverter can take upto 5 seconds to shut down following power loss.
Not only that, but I don't really understand why they were talking about a 300mA RCD (for the arrangement they were postulating), rather than a bog standard 30mA RCD or RCBO? Am I missing something?Strikes me you need to get a competent and experienced electrician to sort this out. That price is far more than a 300 mA RCD would cost to a commercial operation.Billy Wolf said:They then found out that the 300ma RCD would cost about £380, so have ditched that idea due to cost
Quite so. From what little we know, it sounds quite frightening.If they are trading safety against costs then they should not be selling and/or installing equipment about which they appear to lack essential knowledge as they cannot make informed decisions about how far safety is compromised.
AIUI grid tie inverters are deliberately designed not to "free run" in the event that they lose the connection to the grid to protect electricity company engineers.There would be no reason for the invertor to shut down as long as it has power coming from the solar array.
In an ideal world the connection between invertor and the incoming supply should be disconnected by a FIT connection unit when loss of network supply is detected. The FIT connection unit may be in the same "box" as the invertot but it's function is separate from that of the invertor.AIUI grid tie inverters are deliberately designed not to "free run" in the event that they lose the connection to the grid to protect electricity company engineers.
If you have his details, input them here http://www.competentperson.co.uk/, thst will tell you whether he or the company is a member of a scheme provider and if so, I would inform the electrician, that you are making a formal complaint about his standard of work.Thanks for all for the replies. I am trying to get the electricians back but not succeeded so far!
Anything plugged in is best unplugged, as you need to remove both neutral and live from appliances, the switch on a socket outlet is likely only to take the live conductor of the appliance, but some socket outlet are double pole but most are not.To remove all loads from live and neutral - does this mean unplugging all appliances?
Generally cooker isolators are double pole and as you have a dedicated circuit I would guess yours was also.Is switching off the cooker at the isolating switch ok? (The cooker is about 2 years old).
You would require special equipment, portable appliance testing would help diagnose an appliance fault.Is there any other way of testing appliances for the sort of problem which could cause an RCD trip? (I guess not...or I would need specialist equipment...)
In an ideal world the connection between invertor and the incoming supply should be disconnected by a FIT connection unit when loss of network supply is detected. The FIT connection unit may be in the same "box" as the invertot but it's function is separate from that of the invertor.AIUI grid tie inverters are deliberately designed not to "free run" in the event that they lose the connection to the grid to protect electricity company engineers.
The invertor may still run to provide power to the house while the network supply is not available . When network supply is restored the connection unit must synchronise the invertor's sine wave to that of the network sine wave before reconnecting invertor to the incoming supply.
It does seems that cost constraints and marketing pressures have led to installations that may not be ideal.