disconnected cable going out from rcd, IR tested at 500V with everything disconnectedI agree with Bernard.
I would be very surprised from your description if it wasn't a neutral to earth fault after the RCD. Sure, it could be a bad RCD but you said it tested fine so I find that unlikely.
One thing not mentioned yet is that a neutral to earth fault usually means a low resistance or short between CPC and neutral wires, but it could also just be a neutral wire touching anything "grounded".
I would disconnect the lights and extractor wiring from the RCD and do a normal insulation resistance test between neutral and CPC etc. on all the cables downstream of the RCD and take it from there.
N-E= >999Mohm
L-N= >999Mohm
L-E= >999Mohm
so every reading is good but it’s still confusing as to why it’s tripping.