When I was still an apprentice, I can remember an RCD nuisence tripping during the night - every night.
To cut a huge fault finding story short......
It was due to an overhead neutral being lost on a PME supply in the adjoining property. The storage heater load travelling down the main bond to the lead water pipe(I guess), and some of this current travelling out via the cutout in the other house via a N to E fault, tripping the RCD (they where TT). It was fine during the day, as the load next door was low, so only a tiny amount circulated through the property.
To cut a huge fault finding story short......
It was due to an overhead neutral being lost on a PME supply in the adjoining property. The storage heater load travelling down the main bond to the lead water pipe(I guess), and some of this current travelling out via the cutout in the other house via a N to E fault, tripping the RCD (they where TT). It was fine during the day, as the load next door was low, so only a tiny amount circulated through the property.