Remove Rad Help

Joined
21 Aug 2006
Messages
307
Reaction score
3
Location
Buckinghamshire
Country
United Kingdom
Hello All
Tonight i need to remove my rad for the hallway to be replastered.
When i turn the TRV all the way down the rad still gets warm so its not going off fully.
i have removed it and tried to fix but it seems to be off as much as it will go.
if i turn both ends off and drain the rad out is there a fitting that can go on the try valve that will allow me to cap it off until the new one is fitted in a weeks time?
Im thinking of an end screw on cap but cannot think what it is called to search for it
thanks all
 
Sponsored Links
Do you not have the decorators cap for the TRV? its a plastic cap that replaces the TRV head which should close the valve fully.
Also there are brands of TRV that allow a plastic pin to be inserted up under the TRV head to preventing them from closing fully, just check yours hasn't got one of these.
Depending on the size of your rad valve you will need either a 3/4" blanking nut and washer or a 15mm compression stop end, but using only the male (threaded) part of the fitting.
Be aware that if the system is under pressure and the valve isn't closed properly you may get wet when removing the rad. ;)
 
I would replace the TRV then you know its closed properly then add a blanking off cap.

Then when the room gets to temp the TRV will close as its ment to then shut off the heat to the room.
 