Replace Honeywell BDR91 wireless receiver with Nest heatlink

Joined
2 Aug 2017
Messages
2
Reaction score
0
Country
United Kingdom
Hi, need a little help with the heatlink install, read some previous posts but I have a slightly different wiring. On the Honeywell the second L is used. So I have:
N L L A B (C not used)
Do I just ignore the second L connection and connect N L 2 3? or do i also wire it to the heatlink L?



thanks
 
Sponsored Links
The two L terminals are linked together inside the BDR91, so effectively they are the same terminal. Whatever is in both them would go to the single L terminal at the Nest Heatlink.

The wire in the BDR91 A goes to the Heatlink 2

The wire in the BDR91 B goes to the Heatlink 3

Connect the Neutral to N
 