As part of a refurbishment, I'm about to replace this BS3036 fusebox with a CU. There are currently 5 circuits in the 6 slots:
The bottom fusebox is not connected to the mains and I'll be removing that, along with the wiring for 2 storage heaters.
I'll be removing the ring main from arm's length of the kitchen sink and using the 2.5mm² radial for spur isolator switches to
As you can see, space inside the meter cupboard is a bit limited. The cheapest/simplest replacement appears to be a 6-slot CU with a single 30mA RCD/isolator and 5 MCBs. It looks like these would be rated at 6A for each lighting circuit, 20A for the radial and 32A for the ring. Should I use a 40A MCB for the 10mm² cooker point radial?
Ultimately, it is down to the LABC to accept whatever I put in. However, I would appreciate comments and suggestions.
- spare
5A 1.5mm² downstairs lighting radial
5A 1.5mm² upstairs lighting (probably radial)
15A 2.5mm² radial (formerly for immersion heater)
30A 2.5mm² ring
30A 10mm² cooker point
The bottom fusebox is not connected to the mains and I'll be removing that, along with the wiring for 2 storage heaters.
I'll be removing the ring main from arm's length of the kitchen sink and using the 2.5mm² radial for spur isolator switches to
- cooker hood concealed socket
gas igniter concealed socket
washing machine concealed socket
combination boiler fused spur
As you can see, space inside the meter cupboard is a bit limited. The cheapest/simplest replacement appears to be a 6-slot CU with a single 30mA RCD/isolator and 5 MCBs. It looks like these would be rated at 6A for each lighting circuit, 20A for the radial and 32A for the ring. Should I use a 40A MCB for the 10mm² cooker point radial?
Ultimately, it is down to the LABC to accept whatever I put in. However, I would appreciate comments and suggestions.