Are you David Cockburn?It's just a word.
Don't be so precious over words.
Are you David Cockburn?It's just a word.
Don't be so precious over words.
Are you David Cockburn?It's just a word.
Don't be so precious over words.
Can anyone clarify with certainty why 544.1.2 states that, even if there is an insulating section, the bonding should still be connected to the insulated side of the pipework and not the part which is still in the ground?I assume 544.1.2 states what it does is because the disconnection for testing is not going to be done and the regulations still consider that the pipe may be liable to introduce a potential because it is still connected to all of the above mentioned parts.
If anyone else thinks differently perhaps they will say. i'm sure they will
Table 54.8
Minimum CSA of the main Protective bonding
conductor in relation to the neutral of the supply
Says it all, really, doesn't it.but without going to in-depth discussions with the op about why MPB is carried out and why it may not need doing I advised him to do what 99% of electricians would do who don't have an ounce of engineering judgement.
But it does when there is an 'insulating section'.Which talks about main bonding to services entering the building, not metallic parts running through the building.544.1.2
Pragmatism.So basically you want a self-fulfilling prophecy.It is still connected to -
boiler inc. cpcs., CH inc. valves inc. cpcs., gas pipe inc. bonding, MET,
True, but as it cannot, without total disconnection which will not be done, be determined that it is NOT extraneous I assume the powers that be consider it could still be liable to introduce a potential if the complete run of the pipe cannot be verified.If it's only "earthed" because you connect a cpc to it then intrinsically it is not an extraneous-conductive-part.
Agreed, but I only said that to facilitate picturing its purpose.But we aren't talking about supplementary bonding, and there is no indication that this location requires it.consider it supplementary bonding.
Because it is connected to various equipment and CPCs.And why would that be?It will be <22kΩ.
Does that reasoning not preclude all pipework from being an e-c-p?Indeed you would, for it cannot be an e-c-p if you've connected it to the electrical installation.In order to establish if the water service were not now an extraneous conductive part it would be necessary to disconnect it from all of the above mentioned parts to test.
Badly worded.How can it be considered to be introducing a potential when what you've done is to connect it to the electrical installation which by definition it must not be part of for it to be an e-c-p?I assume 544.1.2 states what it does is because the disconnection for testing is not going to be done and the regulations still consider that the pipe may be liable to introduce a potential because it is still connected to all of the above mentioned parts.
In a way, both apply because of the situation.So first you want a self-fulfilling prophecy, and then you want it both ways.That is not a consideration for main bonding.
Do you mean the considerations for a plastic supply and an insulating section are different when it is not possible to verify that a pipe is definitely NOT extraneous?No it doesn't.Either way - 544.1.2 says to connect the bonding.